what is meant by MCB and MCCB? and what its full form?
Answers were Sorted based on User's Feedback
Answer / nilkanth tailor
MCB stands for MINIATURE CIRCUIT BREAKER with rated current
below 100 amperes whereas MCCB stands for MOULDED CASE
CIRCUIT BREAKER with rated current from 10 amperes to 2000
ampers.MCB has breaking capacity upto 10kA, MCCB has
breaking capacity above 10kA.
Is This Answer Correct ? | 143 Yes | 17 No |
Answer / sms
MCB is miniature circuit breaker which is thermal oprated
and use for short circuit protection in small current
rating circuit. MCCB is moulded case circuit breaker and is
thermal operated for over load current and magnetic
operation for instant trip in short circuit condition.
Under voltage and under frequency may be inbuilt. Normally
it is used where normal current is more than 100A.
Is This Answer Correct ? | 70 Yes | 6 No |
Answer / thanigai1984
MCB - MINIATURE CIRCUIT BREAKER with rated current
below 100 amperes whereas MCCB - MOULDED CASE
CIRCUIT BREAKER with rated current from 10 amperes to 2000
ampers.
Is This Answer Correct ? | 43 Yes | 12 No |
Answer / faizal
MCB - miniature circuit breaker
1) we can use it upto 100A
2) thermally operated and used for short circuit/ overload protection
3) trip current / trip characteristics not adjustable it is fixed
MCCB - moulded case circuit breaker
1) we can use it above 100A
2) used for short circuit/ overload protection
3) thermal trip protection for over load current
4) magnetic trip protection for short circuit ( instant operation )
5) trip current / trip characteristics is adjustable
Is This Answer Correct ? | 25 Yes | 6 No |
Answer / nag
mcb mean miniature circuit breaker and mccb mean moulded
case circuit breaker .mcb is used for upto 16A and mccb
used for above 16A .it means it is capable for higher
currents .
Is This Answer Correct ? | 44 Yes | 33 No |
what is rating providing of contactor,relay,fuse unit for motor output power
what is the difference between Resistance VS capacitance
What does Magnetic Neutral Axis
2 Answers Eskom, Genus, Lanco,
1.What is the proper definition of power system stability? 2.some times a blue spark is visible in the secondary side of a distribution transformer at the contact position of bushings and fuse wire,why?
what is the maximum current rating in india for home?
HOW TO CALLICULATE RESITENCE,REACTANCE AND IMPEDENCE VOLTGE OF TRANSFORMER 13.33 KVA 144/240 VOLTS 93/56 A WITH FORMULA
Why dc Supply used in Control circuit.
slor cell made?
whatis mean by voltage?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
how we calculate capacitor bank mvar for 11 kv distribution networ , and i need releation between capacitor bank with voltage, frequency, current, pf
What happens when the field of an alternator connected to infinite bus is suddenly removed?