Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / er sushil saini

this is because whenever fault occur the ac supply will
also fail so protection system will not work and damage to
equipments can occur. DC supply in battery bank will always
be available in case of ac failure and protection system
will work and trip the breakers.

Is This Answer Correct ?    44 Yes 4 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / rd dadhich

1.It is very common practice to use battery with charger for
protection , operation & indication in HT switch gears due
to most relable system to work as after charging only
battery comes directly in line during failure of AC supply.
or power supply.

UPS can be used theoretically , but we are adding one more
week link in critical protection supply due to addition of
inverter. , as inverter is :-

AC supply . > Battery Charger > Battery > Inverter

Where as battery charger is only :-

AC supply . > Battery Charger > Battery

2. AC coils of tripping & closing are un common & bigger in
size.

Is This Answer Correct ?    11 Yes 1 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / kesavan.03

In the case of AC supply we can't reliable. However UPS is
available in any failure of UPS supply also will dangerous
for control system. As in the case of DC supply the battery
is charged & it is available whenever we need. So DC coils
are used for control purpose(Closing & Tripping),

Is This Answer Correct ?    8 Yes 1 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / er. manoj

Now consider a situation when there is a fault and coil supply is given AC, as we know in case of fault there is a voltage dip, so across the coil sufficient voltage would not build up to energize it. So DC is given across tripping or closing coil

Is This Answer Correct ?    2 Yes 0 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / jpgupta

how to check capacitor

Is This Answer Correct ?    2 Yes 0 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / ganesh yeole

hey friends.....I agreed ur ans but I feel one more thing...if we use AC supply to HT system....see you know well sign wave when wave going upper side then down....when wave coming down side you have to see 0 volt but HT tripping or closing coils or contactor pick up time not sufficiently working on there. it not working properly so you found there electrical damages. that's cause DC supply using in HT system. cause DC is directly pick up to coils.........if you are satisfied to my answer you mailed me ganesh.yeole89@gmail.com.......mob no. 09579853838

Is This Answer Correct ?    5 Yes 4 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / ankit

dc supply is used because response time in dc supply is fast as it does not have positive negative sinusoidal wave like ac supply
and in ht we need very fast switching in microseconds

Is This Answer Correct ?    1 Yes 0 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / jp gupta

why can check Ignitor thas its ok or not

Is This Answer Correct ?    0 Yes 0 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / satyanarayana

Suppose if breaker was tripped on under voltage then Ac supply is not available at that instant so that breaker will not trip if AC supply is used for breaker closing and tripping.

Is This Answer Correct ?    1 Yes 1 No

Why dc supply is used for closing and tripping coil of ht breakers. What happen if we use only ups..

Answer / avd

Fundamentaly UPS AC supply can be used. But you are
investing more in UPS than the battery charger. Remember
UPS will have inverter section also.

Is This Answer Correct ?    2 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

What is the mulplying factor of trivector meter (11kv) having ct ratio 100/5 amp.

2 Answers  


WHY IN WESTERN COUNTRIES THE ELECTRIC SHOCK IS VERY SLOW AS COMPARE TO INDIA.&IF ANY ONE HAVE CORRECT KNOWLEDGE THEN SEND OTHERWISE NOT

1 Answers  


purpose of flux relay for turbo generator in power plant

1 Answers  


what is the type of pilot wire in pilot relay?

1 Answers  


why capacitance effect is predominant in underground cable transmission and inductance effect is predominant in over head line transmission?

0 Answers  






What is the "IS" for Rising Main?

1 Answers   APTransco, NTPC,


How to maintaine ht motor efficiancy

1 Answers  


by using pump duty, how we will can calculate the motor duty(KW)? is there any standard or formula.

0 Answers   HP,


can we say current flows inside an atom as electron moves inside an atom?

7 Answers   Vedanta,


in the thermal power plant, why we use the condenser (for cooling the steam) when we have to heat the steam again. i mean why we are cooling the steam,

6 Answers  


what is power factor in ac ckt ?

5 Answers  


what is vch ?

1 Answers   CTS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)