Answer / er sushil saini
this is because whenever fault occur the ac supply will
also fail so protection system will not work and damage to
equipments can occur. DC supply in battery bank will always
be available in case of ac failure and protection system
will work and trip the breakers.
| Is This Answer Correct ? | 44 Yes | 4 No |
Answer / rd dadhich
1.It is very common practice to use battery with charger for
protection , operation & indication in HT switch gears due
to most relable system to work as after charging only
battery comes directly in line during failure of AC supply.
or power supply.
UPS can be used theoretically , but we are adding one more
week link in critical protection supply due to addition of
inverter. , as inverter is :-
AC supply . > Battery Charger > Battery > Inverter
Where as battery charger is only :-
AC supply . > Battery Charger > Battery
2. AC coils of tripping & closing are un common & bigger in
size.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / kesavan.03
In the case of AC supply we can't reliable. However UPS is
available in any failure of UPS supply also will dangerous
for control system. As in the case of DC supply the battery
is charged & it is available whenever we need. So DC coils
are used for control purpose(Closing & Tripping),
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / er. manoj
Now consider a situation when there is a fault and coil supply is given AC, as we know in case of fault there is a voltage dip, so across the coil sufficient voltage would not build up to energize it. So DC is given across tripping or closing coil
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ganesh yeole
hey friends.....I agreed ur ans but I feel one more thing...if we use AC supply to HT system....see you know well sign wave when wave going upper side then down....when wave coming down side you have to see 0 volt but HT tripping or closing coils or contactor pick up time not sufficiently working on there. it not working properly so you found there electrical damages. that's cause DC supply using in HT system. cause DC is directly pick up to coils.........if you are satisfied to my answer you mailed me ganesh.yeole89@gmail.com.......mob no. 09579853838
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / ankit
dc supply is used because response time in dc supply is fast as it does not have positive negative sinusoidal wave like ac supply
and in ht we need very fast switching in microseconds
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / satyanarayana
Suppose if breaker was tripped on under voltage then Ac supply is not available at that instant so that breaker will not trip if AC supply is used for breaker closing and tripping.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / avd
Fundamentaly UPS AC supply can be used. But you are
investing more in UPS than the battery charger. Remember
UPS will have inverter section also.
| Is This Answer Correct ? | 2 Yes | 4 No |
WHAT IS THE DIFFERENT BETWEEN MCB & MPCB? & HOW IS USE?
what is the difference between servo voltage stabilizer and general voltage stabilizer?
what is the UPS
how can we check a fully charged battery?
6 Answers BEML, Singareni Collieries,
If MF is 30000, pt ratio is 110 kV/110 v then what is the ct ratio?
How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)
9 Answers Career Excellent Sdn Bhd, Neona, Northern Max Engineering, Sps Renewables, Terasaki, UEM,
is KVAR (not reverse power) relay necessary to protect from excitor field failure on a brushless, synchroneus generator? Some people with previos experince tell me no but the manufacturers tell me it is designed for that purpose. Is it that it is only necessary for brushless generators and not the older style with the slip rings and brushes?
how to calculate Amp, 2 different Amp of batteries? Example: No. of Batteries = 2 Battery voltage = 12V 1st Battery rating = 17AH 2nd battery rating = 30AH between parallel connection then output volt 12v Amp?
What are the protections for safe running of electric generator?
ROC converges if pole and zero lies inside a) origin b) z=1 c) pole d) zero ? Explanation please? if ROC does not converges then?
Why we use circular(Stepped) cross section in transformer core?
why ct secondary side shortlink provided? its open what will happen?while running ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)