how can we find a burden of potential transformer? what
does it effects? how can we calculate rated load of it?
Answers were Sorted based on User's Feedback
Answer / raghavendran
Burden CAn be denoted in VA or in Ohms.Consider that to a PT
secondary we have a relay connected to it.Now the Total
impedance on the PT secondary is given by Zt = Zsec + Zlead
+ Zrelay.where the Zsec is the impedance of the PT
Secondary,Zlead be the impedance of the lead between the PT
secondary and the Relay,Zrelay be the Impedance of the relay.
Now from the VA capacity of the PT,under normal operating
condition of the PT,calculate the secondary current, Isec.
burden interms of VA can be obtained as Zt*Isec.
Burden interms of Ohms can be had from - Rated
VA/((Isec)*(Isec))
As Burden increases beyond the prescribed value, the
accuracy decreases below the allowable value.
| Is This Answer Correct ? | 30 Yes | 2 No |
Answer / tuktuk
Dear Mr.Raghavendran,
Thank you for your answer, I have the same problem but after reading your answer I still have some concerns.
I am really confused. In this case, we do not know the rated burden of the VT. Now we have to calculate the total burden and then selecte the rated value from IEC standards.
__Ztotal, which you mentioned above, is in Ohm or VA?
__Zsec and Zrelay we can get the value from manufacturer but Zlead, is it calculated by this formula: Zlead= (p*L)/S
(where: p is specific resistivity of copper in ohm.mm^2/m; L is length of lead between the PT secondary and the relay in meter; S is the section of lead in sqmm)? Is this true?
__I dont know how can we get secondary current Isec? (I guess Isec=Usec/Zt, isn't it?)
__And Burden in VA = Zt*Isec. As Ohm law, we have P=VI=RI^2=U^2/R, I do not understand the formula that you used to calculate Burden of VT in VA
Hope that you could help me to solve this stuck in my head.
Thank you.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / tuktuk
Dear Mr.Raghavendran,
Thank you for your answer, I have the same problem but after reading your answer I still have some concerns.
I am really confused. In this case, we do not know the rated burden of the VT. Now we have to calculate the total burden and then selecte the rated value from IEC standards.
__Ztotal, which you mentioned above, is in Ohm or VA?
__Zsec and Zrelay we can get the value from manufacturer but Zlead, is it calculated by this formula: Zlead= (p*L)/S
(where: p is specific resistivity of copper in ohm.mm^2/m; L is length of lead between the PT secondary and the relay in meter; S is the section of lead in sqmm)? Is this true?
__I dont know how can we get secondary current Isec? (I guess Isec=Usec/Zt, isn't it?)
__And Burden in VA = Zt*Isec. As Ohm law, we have P=VI=RI^2=U^2/R, I do not understand the formula that you used to calculate Burden of VT in VA
Hope that you could help me to solve this stuck in my head.
Thank you.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / santhoshkumar
Hello Mr.Raghavendran CT purpose to reduce the current rating of the system to measuring purpose and The Sy will be opened they will higher current carrying capacity in SY so conductor size will be high and step up high high voltage generate higher harmonics it will create serious hazardous in CT CKt
| Is This Answer Correct ? | 2 Yes | 8 No |
Are generator action and motor action relates to a particular machine only?
why an ac solenoid valve attract the plunger eventhough we interchanges the terminal?will the ploes changes?
when generator short circuit condition, the current how dissipates. or at short circuit voltage not available then current how can flow?
what is x'mer ,isolation x'mer & yltra-isolation x'mer?????
what ll happen to current if two phases get short circuited
What is the Powar consumption of fan low speed to full speed? is it same ?
What is resolver and glass scale in CNC how they work?
Why voltage regulation of an alternator is negative for a leading power factor?
how does a liquid starter reduce the starting currents?
what is the working of air compressor.
direction of tarbine& genrator
what is load balancing. what maximum load diffence is allowed between phases.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)