Why hunting will occour in control valve?

Answers were Sorted based on User's Feedback



Why hunting will occour in control valve?..

Answer / s vedpathak

Control valve is used in close loop control system.If it is
hunting , then to troublshoot first put loop for few sec in
manual mode, still if v/v is hunting then it is field
problem i.e v/v or I/P converter problem.

If it is not hunting in manual mode, then the problem can
be either the loop process variable(PV) is hunting or if PV
is ok, either the load/process is varied or loop needs
tuning.

Is This Answer Correct ?    57 Yes 1 No

Why hunting will occour in control valve?..

Answer / kumar

1)I/P PROBLEM
2)INSTRUMENT AIR LEAK(Signal)
4)FLOW DISCHARGE FROM THE PUMP MAY FLUCTUATING.

Is This Answer Correct ?    15 Yes 2 No

Why hunting will occour in control valve?..

Answer / mahesh kumar

Hunting Occur in theControl Valves due to inproper tuning
of PID loop, to remove thr hunting & for smooth operation
Tune the PID loop by adjusting the Gains

Is This Answer Correct ?    17 Yes 7 No

Why hunting will occour in control valve?..

Answer / sam.r

An undesirable oscillation of appreciable magnitude,
prolonged after external stimuli disappear. hunting is the
evidence of operation at or near the stability limit.

in control valves is caused by the oscillation in the
loading pressure to the actuator caused by the instability
in the control system or the valve positioner .

Is This Answer Correct ?    5 Yes 2 No

Why hunting will occour in control valve?..

Answer / sujitkumarnaik@indiatimes

if there is haunting in c/v that means there is disturbance
in i/p signal & o/p signal or feed back.so firstly calibate
it n observe.if still same prob. coming,adjust the pid tunning.

Is This Answer Correct ?    4 Yes 3 No

Why hunting will occour in control valve?..

Answer / mostafa abo el-kasem

Several reasons can cause valve hunting; it can be from signal or from hard ware
To define:
1- Check controller o/p is stable while valve “you can put it in manual mode” is hunting or not (if not stable then it could be from the configuration or from PV change, you can check transmitter/damping/configuration,)
2- If signal is ok ,then it will be hardware problem from
a. Feedback arm not fixed
b. I/P problem
c. Diaphragm damage
d. Flow irregularities
e. Positioner tuning

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

what is full form of SMART

46 Answers   Infosys, ITC Infotech, Lanco, Rosemount, Solvay,


How to calibrate Toxic gas detector?

0 Answers   Supertech,


what is the difference between magnetic flow meter and mass flowmeter

0 Answers  


Q- In the process of checking AC through Phase Tester our body is the part of circuit but we don't recevie Shock, Why ?

2 Answers  


describe flow nozzel principle?

0 Answers   SEWA,






Hi, I am Newely Joined in Construction company instrument engineer? Any one can Plz tell me How can I advanced preparation for Releated Engineering and construction Documents?

0 Answers  


what is the difference between hub and switch?

6 Answers  


generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

1 Answers   Indian Steel,


WHAT IS MEANT BY SUPERVISORY CONTROL?

3 Answers  


Range 8 Kg/cm2, alarm to be set at 2Kg/cm2, at wat pressure reciever switch to be calibrated? justify the ans?

3 Answers  


What is derating factor in Motor?

1 Answers  


tell me the field & lab calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter, temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue),

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)