Why hunting will occour in control valve?
Answers were Sorted based on User's Feedback
Answer / s vedpathak
Control valve is used in close loop control system.If it is
hunting , then to troublshoot first put loop for few sec in
manual mode, still if v/v is hunting then it is field
problem i.e v/v or I/P converter problem.
If it is not hunting in manual mode, then the problem can
be either the loop process variable(PV) is hunting or if PV
is ok, either the load/process is varied or loop needs
tuning.
| Is This Answer Correct ? | 57 Yes | 1 No |
Answer / kumar
1)I/P PROBLEM
2)INSTRUMENT AIR LEAK(Signal)
4)FLOW DISCHARGE FROM THE PUMP MAY FLUCTUATING.
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / mahesh kumar
Hunting Occur in theControl Valves due to inproper tuning
of PID loop, to remove thr hunting & for smooth operation
Tune the PID loop by adjusting the Gains
| Is This Answer Correct ? | 17 Yes | 7 No |
Answer / sam.r
An undesirable oscillation of appreciable magnitude,
prolonged after external stimuli disappear. hunting is the
evidence of operation at or near the stability limit.
in control valves is caused by the oscillation in the
loading pressure to the actuator caused by the instability
in the control system or the valve positioner .
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sujitkumarnaik@indiatimes
if there is haunting in c/v that means there is disturbance
in i/p signal & o/p signal or feed back.so firstly calibate
it n observe.if still same prob. coming,adjust the pid tunning.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / mostafa abo el-kasem
Several reasons can cause valve hunting; it can be from signal or from hard ware
To define:
1- Check controller o/p is stable while valve “you can put it in manual mode” is hunting or not (if not stable then it could be from the configuration or from PV change, you can check transmitter/damping/configuration,)
2- If signal is ok ,then it will be hardware problem from
a. Feedback arm not fixed
b. I/P problem
c. Diaphragm damage
d. Flow irregularities
e. Positioner tuning
| Is This Answer Correct ? | 1 Yes | 0 No |
how to calculate orifice sizing? and tell me if pipe size bet 50mm t0 200mm then we can use pipe flange??? and above 250mm pipe size should i use D & D/2 Flange? is it right or wrong?
IF ASK IN THE INTENVIEW WHAT TYPE OF BMS YOU USE?
where we are used split range control
How to define the size of control valve?
Difference between 2-Valve Manifolds, 3-Valve Manifolds and 5-Valve Manifolds 3 with diagram
what is The specifications for oriface instalation
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
what is meant by Valve reversibility?
How many types of Control Modes in process control, plz tell me all.....?
What is the three element? And how it work?
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
Condensation within a sight glass? Would you expect there to be more problems when using a sight glass if there is condensation on the inside or the outside of the glass, and why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)