Answer / s vedpathak
Control valve is used in close loop control system.If it is
hunting , then to troublshoot first put loop for few sec in
manual mode, still if v/v is hunting then it is field
problem i.e v/v or I/P converter problem.
If it is not hunting in manual mode, then the problem can
be either the loop process variable(PV) is hunting or if PV
is ok, either the load/process is varied or loop needs
tuning.
| Is This Answer Correct ? | 57 Yes | 1 No |
Answer / kumar
1)I/P PROBLEM
2)INSTRUMENT AIR LEAK(Signal)
4)FLOW DISCHARGE FROM THE PUMP MAY FLUCTUATING.
| Is This Answer Correct ? | 15 Yes | 2 No |
Answer / mahesh kumar
Hunting Occur in theControl Valves due to inproper tuning
of PID loop, to remove thr hunting & for smooth operation
Tune the PID loop by adjusting the Gains
| Is This Answer Correct ? | 17 Yes | 7 No |
Answer / sam.r
An undesirable oscillation of appreciable magnitude,
prolonged after external stimuli disappear. hunting is the
evidence of operation at or near the stability limit.
in control valves is caused by the oscillation in the
loading pressure to the actuator caused by the instability
in the control system or the valve positioner .
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sujitkumarnaik@indiatimes
if there is haunting in c/v that means there is disturbance
in i/p signal & o/p signal or feed back.so firstly calibate
it n observe.if still same prob. coming,adjust the pid tunning.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / mostafa abo el-kasem
Several reasons can cause valve hunting; it can be from signal or from hard ware
To define:
1- Check controller o/p is stable while valve “you can put it in manual mode” is hunting or not (if not stable then it could be from the configuration or from PV change, you can check transmitter/damping/configuration,)
2- If signal is ok ,then it will be hardware problem from
a. Feedback arm not fixed
b. I/P problem
c. Diaphragm damage
d. Flow irregularities
e. Positioner tuning
| Is This Answer Correct ? | 1 Yes | 0 No |
WHAT DO WE MEANT BY INSTRUMENT MAINTENANCE IN SOFTWARE SIDE.
Can anyone say that formula of Converting the Diff. Pressure into Flow in Kg/Cm2 or any explaniation of Orifice Plate, Beta Ratio , How to calculate
What s the exact height of installed transmitter?
How to decrease opening & closing time of on/off valve?
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
how to work static pressure sensore how to work dpt
pls send me the 10 years technical question papers of NTPC AND BHEL
15 Answers Bhel, NTPC, ONGC, UCE,
In turbine what does term CDP, NI, NH, HSSOC means.
what is the exact job for automation enggineer?
what is the principal of flow transmeter,level trans meter,presser transmeter?
Explain about 4 wire instrument concept & tell about its wiring fron sensor in Field to PLC panel.Explain with an example?
What is the cascade control
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)