How to make position transmitter feedback reverse i.e at
valve close i want 20ma output and at full open 4ma.for the
NELES positioner,model:ND8261/TS1.
Answers were Sorted based on User's Feedback
Answer / guest
removed link from actuator than fix back which condition
you need you will get other wise if you have HART base
change your counter (first read counter ) than increased
from potentio meter you can? i donot have idies about same
your positioner model but you can try
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / shabeerali
1. Reverse the potentiometer wire connection of position
transmitter.
2. Perform calibration. if required adjust zero and span .
then position transmitter gives reverse feed back
For direct feedback brown, red, orange.
for Reverse feedback orange, red, brown.
pls refer the manual
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kiraninst
If there is PLC/ Dcs then simply change the gain for reverse -1/ reverse action
Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between PLC and DDC?
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
What are SMART insuments?
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.
Please explain for RS 485 & RS 232 communication
What is the different between of rtd and thermocouple ?
How to calibrate DP transmitter by using HART communicator ?
For an Instrumentation Engineer, is there any effect on Instruments of safety zones like zone0, zone1, zone2. As an instrumentation Engineer, what we have to consider or remember while working in these areas.( zones 0,1,2).
What is the difference between HMI and Scada?
Identify and use the ANSI/ISA-S5.1 consensus industrial standard process symbols.
i am having information technology branh ....... can i prepare for psu exam
how to measure low temperature(<100 dec celsisus) with non condact sensor