Answer / k.prakashchandra
A synchronous gen becomes a synch condenser when it runs as
a motor. The current drawn leads the applied voltage.
| Is This Answer Correct ? | 2 Yes | 1 No |
Close the turbine / prime mover , while running in parallel
with other generators/ grid . Vary the excitation to get the
required leading KVAr
| Is This Answer Correct ? | 0 Yes | 0 No |
what meant by Locked Rotor Current ?
Is there thumb rule to calculate how many Insulators to be used for Transmission line of different volatges
what is meant by crawling??
What is the actual meaning of thermal power efficiency ?
why the weight of oil in transformer is specified (on the nameplate) in litres as well as kilo grams?
what is the path of thunderlightening? once both a buffalo and a person were standing 5m apart but lightening hit and killed buffalo not person?
Why usually in all electrical equipment taking more current in Y pahse like pumps,compressor,or any other applications
How can you sized or estimate the ligthning arrester current rating?
why we use 3 phase in our country?..why no 4,5 or 2??
I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....
1)what is the function of a frequency inverter? 2)If a few frequency inverter are connected onto a device network,what are the two setting that will ensure the frequency inverter work properly on the network. 3)whats is the name of the input sensor for weigher? 4)How to confirm that the load cellis faulty? 5)Describe briefly the steps to validate that the weigher is working properly? 6)Describe the procedure to validate the flowmeter accuracy? 7)Describe briefly the steps to validate that the tempreture sensor/transformer is working properly. 8)what is the adjustment that need to be done when you are calibrating the temperature transmitter ? 9)what are the safety measures to be taken before disconnecting motor for rewinding. 10)whats is the synchronous speed in rpm of typical 4pole 50hz motor? 11)whats is the formula for kw, ohm's law 12)if a 3phase motor is rated 3kw,415vac,what is it's rated ampere?
CAN WE GENERATE AC WITHOUT DC EXCITATION?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)