how to select earthing wire? procedures and parameters?
Answers were Sorted based on User's Feedback
Earth wire should be capable of carrying at least ,the full
load current . It can be of cu ,Al or GI.
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / kathiravan
actually the earth conductor capacity not lees than twice
that of FLC of connected load.In india normally cu and GI
flats are used more than 35kw where as open cu wires and GI
wires.The motto of earthing is that "Human Protection" means
the fault current has to be earthed in safe manner.
| Is This Answer Correct ? | 4 Yes | 4 No |
How to calculate rated currennt Of Mcb for 2hp motor...
how to calculate the magnetizing current of ct ( 800A/1A) for Relay 64
How many power required for 1.5 to Airconditioner?
1 Answers College School Exams Tests,
What is the formula to calculate the no load current of a single & three phase induction motor
How is the resonant peak, resonant frequency, and bandwidth determined from nichols chart?
What is different between hypo test and megger test
what is meant by impedance & transient protection?
A parallel flow heat exchanger will perform better than a counter flow heat exchanger. State if the statement is true or false.
Why induction motor overheated?
2 Answers HVCC, Physical Research Laboratory (PRL),
Why wind turbines wheels rotate constantly
What is working principle of washing machine?
why we usually call 415 volts instead of 440 volts
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)