in 5 mva transformer 33/11 kv s/s what rating of capacitor
bank is required & what is the fourmula for rating
Answers were Sorted based on User's Feedback
Answer / sunil sonawane
In 5MVA Transformer 33/11 KV S/S 4.8 MVAR Capacitor bank
should use & its formula is QC= P{tan[acos(pf1)]-tan[acos(pf2)]}
Is This Answer Correct ? | 8 Yes | 5 No |
Answer / swaroop
P.f correction depends on load of secondary. But if you want to compensate on no load it depends on no load pf.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / siva_tyj@yahoo.co.in
Since Transformer losses depend upon the core loss and copper
loss we don't require any capacitor.
Is This Answer Correct ? | 5 Yes | 13 No |