in 5 mva transformer 33/11 kv s/s what rating of capacitor
bank is required & what is the fourmula for rating
Answers were Sorted based on User's Feedback
Answer / sunil sonawane
In 5MVA Transformer 33/11 KV S/S 4.8 MVAR Capacitor bank
should use & its formula is QC= P{tan[acos(pf1)]-tan[acos(pf2)]}
| Is This Answer Correct ? | 8 Yes | 5 No |
Answer / swaroop
P.f correction depends on load of secondary. But if you want to compensate on no load it depends on no load pf.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / siva_tyj@yahoo.co.in
Since Transformer losses depend upon the core loss and copper
loss we don't require any capacitor.
| Is This Answer Correct ? | 5 Yes | 13 No |
what is purpose of using reactor in substations
What is IDMT? What is the principle
What is q factor?
What is the use of core in the transformer?
i have 3500 amp load and select current transformer and perches.how i calculate .please understand
What is the difference between EARTH & NEUTRAL?
can u name the different types of motors used in different types of applications?
what are trouble functions of transformer?ex. prv trip,oltc,oti,wti.explain detail.
can any one tell me the formula for calculating the power and unit consumpetion
What is a thermocouple, and it working principle?
Distribution Transformer are connected in configuration? a. Star/delta b. delta/star c. star/star d. delta/delta
Why transformer is rated in kva?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)