Why is it that variation allowed in supply voltage to
motors is (+ or -)10 %, whereas that in frequency is (+ or -
)5 %
Answers were Sorted based on User's Feedback
Answer / gajendran.al
Variation in supply voltage to motor affects the torque
produced by the motor and is not affected much with +/- 10%
whereas variation in frequency affects the speed of the
motor. Even 1Hz variation could vary speed by 30 rpm for a
4 pole motor. So variation in frequency is not advisable in
motor
Pl note that increase in supply frequency makes the motor
rotate above rated speed which may cause mechanical failure
of motor.
| Is This Answer Correct ? | 6 Yes | 0 No |
For the motor we are not using ups power supply
In ups power supply, we can maintain the voltage as well as
frequency.
But we are using raw power for motors in plants.
Eg if I we are using some load. Now I getting 415 volts at
full load if I reduce some load any reasons then voltage
will lightly increase so voltage will not stay constant.
For that reasons operating voltage +/- 10 %
Shriram....
| Is This Answer Correct ? | 0 Yes | 2 No |
Can we connect two CT'S to one energymeter?
how to check ac servo motor
how hydrogen or helium is a cooling agent for alternator./ generator of big size.
exolain the star delta connection
kindly send me 11KV MV motor differential protection procedure by primary injection method.
What happen if you keep open the Neutral Grounding Switch in open condition of the HT Generator at starting and again on load if it open then?
voltmeter kya hota hy ?
WHAT ARE THE DFT AND RMS MEASURMENTS PRINCIPLE IN NUMERICAL TECHNOLOGY OF POWER SYSTEM ?? WHICH IS BETTER IN WHICH QUANTITY MEASURNMENT??
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
why we measure output of transformer in kva?
What is the difference between SSR drive& AC drive?
why we not used 11kva as a direct our electrnics component.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)