2.5mva transformer is installed in our company with oltc
but it is not working in auto mode ,it is operative in
manual mode control wiring is done how can i rectify it?
Answers were Sorted based on User's Feedback
Answer / s. venkateswararao
check the selector switch auto mode comand, and auto tap
changer time setting lower and upper voltage level setings
to be checked.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naveen
Oltc worked with reverse- forward motor starter through in built programmed pcb card ,command taken from this card as per voltage observation whether voltage level to be raised or down .Voltage level can be also manually controlled via selector switch.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / guest
I feel its better to call in the experts. Like when I
worked at Reliance, the transformer was supplied by Bharat
Bijlee and their person used to come and do the needful
from Kalwa, Mumbai. Its quite complicated and not easy. So
you are advised to consult your supplier.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / ams
check AVR setting and check whether AVR is executing the
command correctly.If yes go for further check.
| Is This Answer Correct ? | 0 Yes | 2 No |
Once you can try changing phase sequence of tap changing
motor.
| Is This Answer Correct ? | 0 Yes | 4 No |
How to check phase R,Y,B
what is the terminal voltage of dc series generator running at rated speed at no load?
Alternator rotor earth fault relay circuit
what is thresold of perception
what is data block in plc ? How the values of data block are written and read by hmi ? what is the difference between function and function block ?
A 6.6 KV/ 440V Xformer. what are the imporatant parts & equipment required for it's protection panel.
sir what is the minimun earth resistance value of an industial bit and grid bit ? and Why?
STATE WORKING OF VACCUM CIRCUIT BRAKER?
why the rating of a transformer in kva not in kw.
Explain the function and difference of Restricted earth fault, simple earth fault and sensitive earth fault with connection diagram.
Where we can use 3.5c cables instead of 4c cables.Why?
why a motor rating in KW?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)