2.5mva transformer is installed in our company with oltc
but it is not working in auto mode ,it is operative in
manual mode control wiring is done how can i rectify it?
Answers were Sorted based on User's Feedback
Answer / s. venkateswararao
check the selector switch auto mode comand, and auto tap
changer time setting lower and upper voltage level setings
to be checked.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naveen
Oltc worked with reverse- forward motor starter through in built programmed pcb card ,command taken from this card as per voltage observation whether voltage level to be raised or down .Voltage level can be also manually controlled via selector switch.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / guest
I feel its better to call in the experts. Like when I
worked at Reliance, the transformer was supplied by Bharat
Bijlee and their person used to come and do the needful
from Kalwa, Mumbai. Its quite complicated and not easy. So
you are advised to consult your supplier.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / ams
check AVR setting and check whether AVR is executing the
command correctly.If yes go for further check.
| Is This Answer Correct ? | 0 Yes | 2 No |
Once you can try changing phase sequence of tap changing
motor.
| Is This Answer Correct ? | 0 Yes | 4 No |
why dc is not given to transformer
How you give clearance to a spare feeder.
Why is it that North America uses 60 hz frequency while Europe uses 50 hz?
why do star-delta connection ? why do not connect any circuit direct connection ?
if our motor load is 150 amp v- kv and we want to install capacitor bank then what is the exact value of that capacitor bank that we should install?and how we calculate that
if two transformers are parallel & both have fault short ckt. impedance of 50KA in each case will it increase or decrease show example?
What is the significance of 3.5 core cable ????
8 Answers Intelux Electronics,
What are the conditions for sustained oscillator or what is backhouse criterion?
how to claculate the ups load in KVA pls give the if any fourmoul?
what is the powerfactor
Why do we use series motor to start our car?
why a three phase induction motor cannot run at synchronous speed ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)