2.5mva transformer is installed in our company with oltc
but it is not working in auto mode ,it is operative in
manual mode control wiring is done how can i rectify it?
Answers were Sorted based on User's Feedback
Answer / s. venkateswararao
check the selector switch auto mode comand, and auto tap
changer time setting lower and upper voltage level setings
to be checked.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / naveen
Oltc worked with reverse- forward motor starter through in built programmed pcb card ,command taken from this card as per voltage observation whether voltage level to be raised or down .Voltage level can be also manually controlled via selector switch.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / guest
I feel its better to call in the experts. Like when I
worked at Reliance, the transformer was supplied by Bharat
Bijlee and their person used to come and do the needful
from Kalwa, Mumbai. Its quite complicated and not easy. So
you are advised to consult your supplier.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / ams
check AVR setting and check whether AVR is executing the
command correctly.If yes go for further check.
| Is This Answer Correct ? | 0 Yes | 2 No |
Once you can try changing phase sequence of tap changing
motor.
| Is This Answer Correct ? | 0 Yes | 4 No |
WHAT IS THE DIFFERENCE BETWEEN UNDERVOLTAGE COIL, CLOSING COIL AND SHUNT TRIP COIL OF AN ACB?
State The Difference Between Generator And Alternator?
rrb question
What is reactive power and where it is used.
in 33kv/11kv stepdown t/f why should we use Star point
How to set a Zone 1 distance relay for distribution feeder?
0 Answers Schweitzer Engineering,
What is meaning of DRU in gen.of AVR.
why we create vaccume in transformer tank before oil filteration?
why can not run two different phase circuit in to the same conduite
How the power factor is more in high speed machines
how will you calculate rated Primary and Secondary voltage and Current for 2500 KVA, 11kv/443V Transformer
if a 3phase motor runnig in star delta starter with full load of its,and its rated 15 amps.now we conneted over load thermal relay at its main contactor,here what will be our amps sittings?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)