Answer / ekailash
4-20 mA is a standard range used to indicate measured
values for any process. The reason that 4ma is chosen
instead of 0 mA is for fail safe operation.
For exa.- a pressure instrument gives output 4mA to
indicate 0 psi, up to 20 mA to indicate 100 psi, or full
scale. Due to any problem in instrument i.e. broken wire,
its output reducess to 0 mA. So if range is 0-20 mA then we
can differentiate whether it is due to broken wire or due
to 0 psi.
Is This Answer Correct ? | 9 Yes | 0 No |
Thank u Mr.EKailash .I think it is required answer.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the technical name of minute currents that i have been produced in moving electrical objects?
Shall we get electrical shock if we touch the positive terminal of a 230 volt dc supply?
what are the method of testing of transformer??
Can any body tell me the different types of LT cables & their application.
what is the length of air terminal in lightening arrester system.
how we can check the CT & VT?
What are the disadvantges of leading power factor
what is post close & pre close of trip circuit supervision relay in circuit breaker control scheme?
how many test is necessary for 27mva transformer.
electrical resistance in human body?please dedails quick. mail.psrinivasan20@yahoo.com
Actually I have a doubt on neutral and earth.we use Ac power without taking neutral by connecting to earth,but at that time does it affects on efficiency of any electrical components or no? If yes how?
in slip ring motor if motor specification is given how we calculate its rotor resistance in starting