Answer / ekailash
4-20 mA is a standard range used to indicate measured
values for any process. The reason that 4ma is chosen
instead of 0 mA is for fail safe operation.
For exa.- a pressure instrument gives output 4mA to
indicate 0 psi, up to 20 mA to indicate 100 psi, or full
scale. Due to any problem in instrument i.e. broken wire,
its output reducess to 0 mA. So if range is 0-20 mA then we
can differentiate whether it is due to broken wire or due
to 0 psi.
Is This Answer Correct ? | 9 Yes | 0 No |
Thank u Mr.EKailash .I think it is required answer.
Is This Answer Correct ? | 0 Yes | 0 No |
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?
what is working parincipal of a ht transformer
How the flights will be fly be fly without ground connection under raining with thunder lighting?
Can anyone please give me the parameters , formula needed to calculate the circuit breakers for building services.Thanks
please send me privious exam's queation papers of section engineer(electrical).
Why short circuit calculation is not required in LT cable sizing and requiredin HT cable sizing only
What is Instantaneous Earth fault relay,how will work
how to interlock 3 incomer-ACB,1 buscoupler ACB,... pls answer this question and if possible send me the ckt diagram..haifriends2910@gmail.com
what is the working and construction of generator
What is the difference between single core 2 wire and single core 3 wire system? Which application we are using this? and for What purpose we are using this?
what is softstarter?
How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99