Answer / c r venkatesh
Absolutely no problem.you can always use higher burden CT'
without any problem
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / roy
Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / chandru_williams
no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anbuselvan
No problem.
Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.
So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.
Here both your current rating is same.so no problem at all,
even if the voltage varies.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / satvinder kumar
50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE
| Is This Answer Correct ? | 1 Yes | 1 No |
basic of electrical information where i can get? plz send the website which you know?
Why carbon brushes are used in motors?
Comparative difference between 33Kv & 66KV for transmitting the load of 7 MW at a distance of 34 Km.
What could be the problem if two power transformers trip on stand by earth fault at same time
Give accurate definitions for these electric terms: Inductor Inductance Inductive Induction Reactance Reactive Esam Baraka ٢١ ساعة
what is sevice settings for mccb?How can be it setted?
what is the electrical?
A long transmission line is limited by - a)thermal limited b)voltage limited c)stability limited d) L,C limited please explain with proper reason.
if flux and load static in dc motor and supply voltage increases 20% then what happened in speed
Difference between directional over current and non directional over current ?
what is difference b/t ac current and dc current
4 Answers L&T, Meghana Engineers,
Differentiate between low pass, high pass and band pass filter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)