My requirement is 1VA,50/5A Current Transformer for
Metering .If I select 15VA , 50/5A CT.Is there any
possibility of Technical Problem ?
Answers were Sorted based on User's Feedback
Answer / c r venkatesh
Absolutely no problem.you can always use higher burden CT'
without any problem
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / roy
Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / chandru_williams
no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anbuselvan
No problem.
Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.
So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.
Here both your current rating is same.so no problem at all,
even if the voltage varies.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / satvinder kumar
50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE
Is This Answer Correct ? | 1 Yes | 1 No |
int a,b ; a=b=10 ; if(a>b){ printf ("%d",a)}; no error output is a=10
If VFD is On but no starting commond on it. so how many outpout voltages of VFD
what is the importance of neutral in elctrical system?
4 Answers IOCL, Kharafi National,
Give two basic sprrd control scheme of DC shunt motor.
Alternator rotor earth fault relay circuit
How we calculate the size of ht cable for any transformer
In our homes we place the 5Amps fuse...now in our house only takes 5Amps for all normal conditions ha???
What will be the minimum megger value of 1700 KVA Transformer? a) Do megger value varies according to climate conditions and area . b) If megger value is 100 mega ohm is it good for new transfomer. Explain?
Isolation transformer primary to sec turns ratio?
How does a tertiary winding filter harmonic(espcially 3rd one) from entering into load system?
what will happened to give the dc supply to ac transformer?
what is use of mccb.