Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


My requirement is 1VA,50/5A Current Transformer for
Metering .If I select 15VA , 50/5A CT.Is there any
possibility of Technical Problem ?

Answers were Sorted based on User's Feedback



My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / c r venkatesh

Absolutely no problem.you can always use higher burden CT'
without any problem

Is This Answer Correct ?    11 Yes 1 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / roy

Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44

Is This Answer Correct ?    3 Yes 0 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / chandru_williams

no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.

Is This Answer Correct ?    3 Yes 1 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / giri

No problem ,but the size of CT may increase.....

Is This Answer Correct ?    2 Yes 1 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / anbuselvan

No problem.

Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.

So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.

Here both your current rating is same.so no problem at all,
even if the voltage varies.

Is This Answer Correct ?    2 Yes 1 No

My requirement is 1VA,50/5A Current Transformer for Metering .If I select 15VA , 50/5A CT.Is there..

Answer / satvinder kumar

50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

What is the diffrece between ACB & MCCB

8 Answers  


which circuit breaker enclosure is best for maintenance guy? 16 bolt & 20 bolt squre or 16,20 bolt hinge

2 Answers  


i have 2 motor of same rating. on no load condition one motor take 1.6A but other motor is taking 4.8A. what is the reason of this. please explain with proof.

8 Answers   Ambuja, UltraTech,


Difference between HRG and NGR. Are they both the same thing

0 Answers  


how do you select the ct/pt rating in substation

1 Answers   Apollo, Shreem Electric Ltd, Tata Motors,


What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing?

1 Answers  


Upload data by LSMW via BAPI in SAP system.

1 Answers  


At what condition differential relay will act in transformer and ht motor?

1 Answers   Equate,


what is the safety points of vaccum circuit breaker.

0 Answers  


I want to make street light with solar system ... What may I do for procedure and how much of estimation for each material ... If any one knows guide me and inform this id : aravindd7@gmail.com

0 Answers   Suzlon,


can we use inductor for passing or blocking of AC or DC?

3 Answers   Moser Baer, NTPC,


how to set earth fault relay

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)