My requirement is 1VA,50/5A Current Transformer for
Metering .If I select 15VA , 50/5A CT.Is there any
possibility of Technical Problem ?
Answers were Sorted based on User's Feedback
Answer / c r venkatesh
Absolutely no problem.you can always use higher burden CT'
without any problem
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / roy
Hi ,
Yes there is . and a highr rated VA is never recommented
for metering ( again it depends the accuracy but still not
used as per IEC)
Note:The accuracy class will not be guaranteed for burdens
above rated burden or below 25% of the rated burden.Check
IEC 60044
Amd more interstingly , we are allowing or excepting to
saturate this metering core during fault to protect the
metering Equipment reff. IEC 44
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / chandru_williams
no problem at all when we increase the burden . But It
should be noted that the current ratio should not be
increased, since it leades to sensing problem which inturn
hinders the metering values.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anbuselvan
No problem.
Bcaz CT is an Instrumental Transformer(i,e.,Measurement of
High rating current) to measure only Current.
So there will be no of tapping for each range of current.So
that it will easily sense the rating which u set.
Here both your current rating is same.so no problem at all,
even if the voltage varies.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / satvinder kumar
50/5 1va is suitable for bar primary ct if you go for
higher 15 va then it is good to opt wound primary ct{WPL}
OTHERWISE THE SIZE OF THE CT WILL INCREASE
| Is This Answer Correct ? | 1 Yes | 1 No |
funtion of choke
What is the latest generation of circuit breakers called?
when voltage gets down the current of motor increases. but according to Ohm's law voltage is directly proportional to current. plz explain
4 Answers Maruti Suzuki, TATA,
how vfd drives energy save
How to calculate approximate load loss of a distribution transformer by knowing %ge imp of transformer?
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.
wat is the difference between rotor 1st stage fault and 2nd stage fault?
When Alarm report at LED,Alarm volatge is 11-13 Volt But LED is of 3 volt.then why not it burn?
what is isochronous mod? what is voltage drop mode and p.f mode?
dear sir, How i calculate the 2 phase welding transformer power or kva?? kindly tell me....
why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage from 33kv to 415v directly using single transformer?
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)