We are using Powerica make 100 KVA DG set. Whenever i
connect compressor on DG load (Compressor Make Atlas Copco
5.5 kva) that time we face the lot of fluctuation on Dg
output. Can you please suggest me how can prevent this
fluctuation?
Answers were Sorted based on User's Feedback
Answer / prajeshkumarbe@yahoo.com
hai to all..,
this is the wonderful question, powerica DG is another
company of Caterpillar .atlas copco also best compressor
designer.
ur Dg is 100KVA , load is 5.5KW (its not a 5.5kva) that
means 7.5 hp,
while getting the fluctuation note it below.,
1.whether fluctuation is comes while starts r stops(loading/
unloading)
2.fluctuation time wt is the pressure (if compressor
reaches maximum working pressure it will takes more current)
3.normally it will be enough DOL Stater ,if its take more
current while start /stop,just u make the Star Delta
stater , surly will get best result.
4.check the DG fuel filter condition ,if its ran above 300
running hrs replace newly
5.DG should be run 80% load max ,
6. give the DG load only compressor itself and measure the
performance
7.ensure the compressor max pressure switch properly working
8.in DG AVR (Automatic voltage regulator) system may failure
9.check the self exciting system rectifier diodes
thanking u all
Rajesh
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajesh
Dear sir,
5.5kva Around (5kw) Capacity is very low
capacity compared to your generator you just calculate
other power usages And load .
If u feel compressor is a only problem you can minimize
other load and start the compressor for testing you can get
conclusion for this issue
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / n. gopala krishna
what type of dg u r using . brushless or brush type if
brush type please check brushes if brushless type check
exitation voltage or some where loose connections in
execitation side
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / elango
the starting current is the only problem which produce a
dip in supply voltage .so higher capacity load must be
started first and next lower loads...
| Is This Answer Correct ? | 2 Yes | 2 No |
why fault current always calculated for 1 seconds?
What accessories required to give the motor with given circuits and do you know the ratings of those accessories?
when neutral will carry the current?what could be the magnitude?
A TRANSFORMER 440/400V,DELTA/STAR CONNECTED.THE NEUTRAL CONNECTED WITH GROUND CABLE THAT IS DIRECTLY CONNECTED TO THE PANEL,FROM PANEL IT IS CONNECTED EARTH PIT.IS IT RIGHT? IF IT IS RIGHT LEAKAGE CURRENT AFFECTED.SECONDATY IS PROTECTED WITH EARTH LEAKAGE RELAY.
why asa method ZPF method is more accurate than ASA method?
What do we use in Motor core laminations..???CRGO or CRNGO..and why..????
How many methods to take IR value of Current Transformer?
any one please tell taht what type questions will be asked in BHEL interview, i am having interview on 24th Dec, please send this to mail pradeepsistam@yahoo.co.in
Why don't connect earth wire to elcb?if earth fault occur,how will detect it
1 Answers TATA, Tata Communications, Telecommunications,
Earth leakage relay basic knowledge principle
what is difference between 5A and 100A CT constructional wise and operation?
why ups rated in kva
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)