Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We are using Powerica make 100 KVA DG set. Whenever i
connect compressor on DG load (Compressor Make Atlas Copco
5.5 kva) that time we face the lot of fluctuation on Dg
output. Can you please suggest me how can prevent this
fluctuation?

Answers were Sorted based on User's Feedback



We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / prajeshkumarbe@yahoo.com

hai to all..,
this is the wonderful question, powerica DG is another
company of Caterpillar .atlas copco also best compressor
designer.
ur Dg is 100KVA , load is 5.5KW (its not a 5.5kva) that
means 7.5 hp,
while getting the fluctuation note it below.,
1.whether fluctuation is comes while starts r stops(loading/
unloading)
2.fluctuation time wt is the pressure (if compressor
reaches maximum working pressure it will takes more current)
3.normally it will be enough DOL Stater ,if its take more
current while start /stop,just u make the Star Delta
stater , surly will get best result.
4.check the DG fuel filter condition ,if its ran above 300
running hrs replace newly
5.DG should be run 80% load max ,
6. give the DG load only compressor itself and measure the
performance
7.ensure the compressor max pressure switch properly working
8.in DG AVR (Automatic voltage regulator) system may failure
9.check the self exciting system rectifier diodes
thanking u all
Rajesh

Is This Answer Correct ?    2 Yes 0 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / rajesh

Dear sir,
5.5kva Around (5kw) Capacity is very low
capacity compared to your generator you just calculate
other power usages And load .

If u feel compressor is a only problem you can minimize
other load and start the compressor for testing you can get
conclusion for this issue

Is This Answer Correct ?    7 Yes 6 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / n. gopala krishna

what type of dg u r using . brushless or brush type if
brush type please check brushes if brushless type check
exitation voltage or some where loose connections in
execitation side

Is This Answer Correct ?    3 Yes 3 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / elango

the starting current is the only problem which produce a
dip in supply voltage .so higher capacity load must be
started first and next lower loads...

Is This Answer Correct ?    2 Yes 2 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / deepak

you have to use softstarter for this problem.

Is This Answer Correct ?    0 Yes 1 No

We are using Powerica make 100 KVA DG set. Whenever i connect compressor on DG load (Compressor Ma..

Answer / rajju

Kindly check the other loads that u r connected because
there may max demand problem

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between earth fault protection of motor feeder with CBCT and Without CBCT ?

0 Answers   Enmas, Michelin, Reliance,


What is the cause for a blown fuse in one phase of primery side(HV) of a three phase transformer( 4169v-460v) in the time of closing its supply breaker. There is no load on the secondery side of the transformer in this moment.

3 Answers   Novachem,


What is the minimum load that you can keep in a 3 Phase 40 KVA Diesel Generator? Is it neccessary to load all the 3 phases? Can a phase be left without load?

2 Answers   DRDO,


What happen while we measure the Current in Rotor?

1 Answers  


what is power and what is watts detailed description and formulas

2 Answers  


how u select control transformer for a mccb panels or any panels?for expample we hav 440 volts maim supply and control volts is 230v?

0 Answers  


how to calculate efficiency of voltage and current controlled welding transformer?

1 Answers  


please send me latest & previous years question papers for IOCL Technical level questions

0 Answers  


In Extended Delta transformer, by which method we can measure the extended angle of transformer?

1 Answers   Usha Martin,


if field breaker of generator is closed prior to its rated speed on a power generating unit. what will be the effect on generator, unit transformer and starting transformer.

0 Answers   Power Plant,


HOW TO CALCULATE THE APFC Panel Design

1 Answers  


explain the meaning of harmonic resonance

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)