We are using Powerica make 100 KVA DG set. Whenever i
connect compressor on DG load (Compressor Make Atlas Copco
5.5 kva) that time we face the lot of fluctuation on Dg
output. Can you please suggest me how can prevent this
fluctuation?
Answers were Sorted based on User's Feedback
Answer / prajeshkumarbe@yahoo.com
hai to all..,
this is the wonderful question, powerica DG is another
company of Caterpillar .atlas copco also best compressor
designer.
ur Dg is 100KVA , load is 5.5KW (its not a 5.5kva) that
means 7.5 hp,
while getting the fluctuation note it below.,
1.whether fluctuation is comes while starts r stops(loading/
unloading)
2.fluctuation time wt is the pressure (if compressor
reaches maximum working pressure it will takes more current)
3.normally it will be enough DOL Stater ,if its take more
current while start /stop,just u make the Star Delta
stater , surly will get best result.
4.check the DG fuel filter condition ,if its ran above 300
running hrs replace newly
5.DG should be run 80% load max ,
6. give the DG load only compressor itself and measure the
performance
7.ensure the compressor max pressure switch properly working
8.in DG AVR (Automatic voltage regulator) system may failure
9.check the self exciting system rectifier diodes
thanking u all
Rajesh
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / rajesh
Dear sir,
5.5kva Around (5kw) Capacity is very low
capacity compared to your generator you just calculate
other power usages And load .
If u feel compressor is a only problem you can minimize
other load and start the compressor for testing you can get
conclusion for this issue
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / n. gopala krishna
what type of dg u r using . brushless or brush type if
brush type please check brushes if brushless type check
exitation voltage or some where loose connections in
execitation side
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / elango
the starting current is the only problem which produce a
dip in supply voltage .so higher capacity load must be
started first and next lower loads...
| Is This Answer Correct ? | 2 Yes | 2 No |
What is servo motor and what are different types of servo motor
what should be the ideal gauge of wire (In sq mm) for different loads in Ampere?
At light load transformer efficiency is less because A secondary output is low B transformer losses are high C fixed loss is high compared to output D copper loss is small
What is surge impedence and surge loading....???
In a flange coupling, the flange bolts are designed for
how to caculate no load loss, load losses & impedance percentage in power or distribution transformers
Why efficiency of generator is higher than motor at a particular load?
what heppend if we are connected u1-v1-w1 as a star point in the place of u2-v2-w2 in power genration
Dear all: Recently we got a question about Interface between PMS and SAP-PM.once we got a update message from PMS.we should set the deletional flag for functional location in SAP system.Is there any FM or BAPI to use?There are only functional location create and change provided by SAP. Best regards!
In a Synchronous generator, Can AC voltage be used instead of DC voltage in field winding of rotor to produce AC power?
how to increase the power factor in machines
diffrence between abcb and mocb
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)