What is the cause for a blown fuse in one phase of primery
side(HV) of a three phase transformer( 4169v-460v) in the
time of closing its supply breaker.
There is no load on the secondery side of the transformer
in this moment.
Answers were Sorted based on User's Feedback
Answer / engr.abdurrahim
As your Question, I think in your transformer is having
interturn fault or single phasing or may be LG
fault.Without load if any fuse blown means connected things
(Transformer)itself having problem.
Solution:
Do the Meggaring and check insulation between, phases at HV
side,LV side,
Check insulation between phase to neutral, Phase to earth.
Check Earth resistance also.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / pillay
It could be just high inrush current,
incorrect fuse size or a defective fuse
in the first place.If it recurs than
further investigations should be taken.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / niranjan
Due to high inrush of current or there may an inter turn
fault on ther primary side of the transformer
Is This Answer Correct ? | 1 Yes | 2 No |
What is the differance between negative dc voltage and positive dc voltage because some circuit uses -24,-5,-12,- 15,volt dc supply
10 Answers eLab, Hero Honda, NTPC, Suzlon, Teradyne,
what is DAR test?
2 Answers Al-Naboodah, ISRO, ONGC,
how capacitor can split the phase.
help!!!! i bought a new house 2 yrs ago,ive just had 2 new lights fitted,when i boil the kettle,maybe 2 times in succession the safety light switch trips out,it dosnt do it straight away but it seems to do it when the kettle boils!!!!! sounds very odd to me
Why high voltage lines (overhead ) are called high tension lines?
ASTM D 3455 - Standard Test Methods for Compatibility of Construction Material with Electrical Insulating Oil of Petroleum Origin has been used for Testing Transformer Oils with a product placed in it. Aged Control Oil has a Power Factor of 0.032% at 100°C. Aged Oil with a Test component has a Power Factor of 0.093% at 100°. Is this increase acceptable? If not why? How much increase is acceptable?
We are using 3core 11KV HT cable for same phase for generator outgoing, the cable leakage current is high and cable heated overly what is the remidy, if we use the 3core cable for 3phases the problem is solved are not?
How can we calculate the capacity of the capacitor bank attached with the Main panel, when we know the capacity of the panel installed in KVA Rating?
why we r used DC megger insted of AC megger?
How to calculate cable size in HT AND LT
Write the analogous electrical elements in force current analogy for the elements of mechanical translational system.
11000volt DG set carnt kaise banvay