What is the cause for a blown fuse in one phase of primery
side(HV) of a three phase transformer( 4169v-460v) in the
time of closing its supply breaker.
There is no load on the secondery side of the transformer
in this moment.
Answers were Sorted based on User's Feedback
Answer / engr.abdurrahim
As your Question, I think in your transformer is having
interturn fault or single phasing or may be LG
fault.Without load if any fuse blown means connected things
(Transformer)itself having problem.
Solution:
Do the Meggaring and check insulation between, phases at HV
side,LV side,
Check insulation between phase to neutral, Phase to earth.
Check Earth resistance also.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / pillay
It could be just high inrush current,
incorrect fuse size or a defective fuse
in the first place.If it recurs than
further investigations should be taken.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / niranjan
Due to high inrush of current or there may an inter turn
fault on ther primary side of the transformer
Is This Answer Correct ? | 1 Yes | 2 No |
What are the limitations of Kirchoff's laws?
How can we calculate the motor frame sizes?
what is electrostatic presipitator in thermal power plant,and why it is used?
Define corner frequency?
why middle phase should used for earth fault and other phases used for over current in overcurrent and earth fault relay?
How many sprinklers should be in one pipe line?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
why fan consume constant power even when we increase or decrease its circuit resistance through speed regulator???
What is meant by knee point voltage?
why autotransformers are not safe for supplying low voltage from a high voltage source?
is it possible to turn on the single phase star delta on delay timer using 24 v dc ?
Why current leads the voltage in case of capacitor load? Why voltage leads the current in case of inductive load? Why both are with in phase in case of restive load?