What is the minimum load that you can keep in a 3 Phase 40
KVA Diesel Generator? Is it neccessary to load all the 3
phases? Can a phase be left without load?
Answers were Sorted based on User's Feedback
Answer / binod barik
3PH 40KVA IS THE O/P OF THE GENERATOR MAX.LOAD WE RECEIVE
IS=40*.8=32KW( TAKING STD. AS COS IS 0.8 OF THELOAD SIDE
POWER FACTOR).TAKING MIN. LOAD MEANS DECREASING ITS
EFFICIENCY. YES IT IS NECESSARY TO GIVE BLANCE LOAD IN 3
PH SIDE TO AVOID HEATING & TO GET MAX EFFICIENCY, SO NO
PHASE LEFT WITHOUT LOAD
Is This Answer Correct ? | 4 Yes | 2 No |