Two alternators say 1 & 2 are poised to parallel operation.
But at the time of paralleing alternator 2 gets out of the
system by tripping Earth fault relay. Please send me reply
why this is happening?
Answers were Sorted based on User's Feedback
Answer / jyotirmoy das gupta
The answer depends on the following parameters: 1. At which
point the two generating systems are earthed, 2. Is there a
neutral isolation for the second generator, 3. how the
earth fault sensing element is connected- by 3 phase CT
forming residual circuit or direct measurement placing the
CT between generator star point and earth, 4. what is the %
setting for earth fault protection and what delay is
setted.
Is This Answer Correct ? | 3 Yes | 1 No |
In addition to the above answer, what type of earthing is
provided for both the generators also matters. Secondly, if
it is NGR, which NGR is closed, or both are closed.
Is This Answer Correct ? | 1 Yes | 0 No |
Difference between 3.5 core and 4 core
how to select energy meter? have any calculation?
why do we use 25kv supply for traction purpose
What is the megger value for ht
how the specific fuel consumption of 320 kva deisel genarator set (explain with formulas please)?
why white color LED light is not possible?
what is the advantage of DC Motor over AC motor & Where its applicable ?
A 60W,250V bulb when connected to a 230V supply will it give more light or less or will be give normal light?
why motors are rated in HP?
what is mean by induction & conduction principle ? how they differ from each other ? thank you
ELECTRICAL DRIVES: can a motor load system with passive load torque can have equilibrium speed in second quadrant
How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?