Two alternators say 1 & 2 are poised to parallel operation.
But at the time of paralleing alternator 2 gets out of the
system by tripping Earth fault relay. Please send me reply
why this is happening?
Answer Posted / jyotirmoy das gupta
The answer depends on the following parameters: 1. At which
point the two generating systems are earthed, 2. Is there a
neutral isolation for the second generator, 3. how the
earth fault sensing element is connected- by 3 phase CT
forming residual circuit or direct measurement placing the
CT between generator star point and earth, 4. what is the %
setting for earth fault protection and what delay is
setted.
| Is This Answer Correct ? | 3 Yes | 1 No |
Post New Answer View All Answers
How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?
What are the uses of lead compensator?
Can Anyone suggest the Standards (IEC or IS) for selecting copper current density?
draw the restricted earth fault protection circuit install on power transformer and identify its parameters and draw C/C curve of it
all the technical question with answers pleas send your email id ramar_eee@yahoo.com
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
How To increase Knowledge Of boliler regarding To Only Electrical Field..
Why using synchronising methed in DG's sets?
I have a reading off 1.5ohms at my mem my main c/b is rated at 40/6 amps in a domestic house and i was told to change it to a b curve c/b is this ok
How to calculate the copper in HT motors if KW, RPM & Voltage is given
How they LT panel busbar size choose
I want to put this query to SENIOR & EXPERIENCED ELECTRICAL ENGINEERS. 1)I want to know about the control circuit diagrams for control panels. I found it difficult to understand. Is there ant booklet through which we can learn the circuit diagrams? 2)I want to learn about conduiting, laying cables, preparing cable schedules and various techniques which is the part of building infrastucture(construction field). I don't have any experience in this area. I have experience in control panels only. that's why i am not getting any opening in building infrastucture (construction field).Can I get the job in this field as Trainee Engineer? How to enter this field? I need job in PUNE
Explain how you decide what size of electrical wire do you need?
Which standard we are following earthing resistance test