why we use 20 KV, 10KA LA on 22 KV Line
Answers were Sorted based on User's Feedback
Answer / dipen patel
b'coz 11,22,33 are phase to phase voltage,LA rating is
phase to neutral.that's y LA rating is always less than
system voltage.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / alok kumar nayak (action ispat
rating of la = line-to-line rms voltage X 1.1 X coefficient earthing = 22X1.1X0.8 = 19.36 =20
10 ka is nominal discharge current that means the surge current that flows trough ihe la after the spark over & it is expressed in crest value of spcife=ied wave (tested).
10ka < 66kv (lighting stroke is high)
5ka < 66kv(lighting stroke is low)
2.5ka > 22kv small substation
1.5ka > 22kv small trafo
Is This Answer Correct ? | 2 Yes | 0 No |
how to calculate the input current in singel phase and 3phase supply to 5kva ups
Everybody Knows What is ACB, VCB but anybody tell me what is ST?
Why the substation measure in KV but not in the power ratings of transformer.
determine two methods to find loose connection in operational electrical system?
why are the transmission lines operated at 220 kv nly... nt les dan dat...
what is the significant for using two types of voltage(line voltage & phase voltage)
Whats the type of current and potential transformers?
how to calculate diesel consumption of a D.G.Set?
sometimes, eventhough the HV side of the transformer is opened there is a voltage in LV side .How is it possible?
what is difference between vcb and mccb
Best way to measure the Soil resistance of rocky soil, three probe method and four probe method
What was your role in the silicon evaluation/product ramp? What tools did you use?