Answer / dipen patel
b'coz 11,22,33 are phase to phase voltage,LA rating is
phase to neutral.that's y LA rating is always less than
system voltage.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / alok kumar nayak (action ispat
rating of la = line-to-line rms voltage X 1.1 X coefficient earthing = 22X1.1X0.8 = 19.36 =20
10 ka is nominal discharge current that means the surge current that flows trough ihe la after the spark over & it is expressed in crest value of spcife=ied wave (tested).
10ka < 66kv (lighting stroke is high)
5ka < 66kv(lighting stroke is low)
2.5ka > 22kv small substation
1.5ka > 22kv small trafo
| Is This Answer Correct ? | 2 Yes | 0 No |
how to calculate the power factor when instantaneous voltage and current has harmonics in it ?
tell me the operation of ELCB. How it detects a fault?
What is the difference between magnetic loading and electric loading of a machine?
Hello sir, pls send me hpcl technical test papers .i am. Appearing for the exam.
1.what is difference in maintain Hz again Hz in USA ? 2.how to calculate the battery AH? 3.why are yearly maintained in transformer how many tests in required?
how much amp MCB is required for 1/2 kva power back up?
How to select power cable for machine
what is the voltage of insulation megger that should be used for measuring the resitance of 66kv equipments.
It is desired to flood light the front of a building 42 meters wide and 16 meters hig.Projectors of 30 degree beam spread and 1000 watt lamps giving 20 lumen/watt are availabl.If the desired level of illumination is 75 lumen/m and show a suitable scheme.Assume the cofficient of utilization, deprecitation factor and waste light factor are 0.4, 13 and 1.2 respectively.
my UPS is 600VA with 0.6 p.f and i use it for my computer which has 450W power supply unit, a monitor of 633nW and speakers. Can any one explain this.. because the output of UPS should be 360W (<450W)
while doing the excitation current test on power transformer what is the value of voltage to be applied? Nomonal rated voltage or 10% of rated voltage? Is it necessary to apply on high voltage side?
What current position are you holding in your current company?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)