sometimes, eventhough the HV side of the transformer is
opened there is a voltage in LV side .How is it possible?
Answers were Sorted based on User's Feedback
Answer / iamdon
This is due to residual magnetism in the core which is
inherenly present.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / avd
I am not agree with you people. Residual magnetism can not
produce any emf. You need a variable flux or rotating
conductor to produce emf, which is not the case.
There will not be any voltage in sec winding if primary is
kept open.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / shyam
bcoz even if the hv(secondary side) is opend there will be
a small amount of flux flows through the core of the
transformer
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / thuranga
we can find voltage on lv side even when we remove hv
side,is because of its residual flux present in the
core......and this can happen only if there is no perfect
grounding to the transformer.
even though the grounding is not present, the voltage appear
for only a short time,as that voltage will get consumed by
the inductance and capacitance on the LV side of the
transformer.
| Is This Answer Correct ? | 1 Yes | 2 No |
What are the different types of trap used for Indian & western Toilets?
If the load of transformer is getting more than its rating,,,than how to overcome this problem? Suppose thee rating of transformer is 315kva and the load is going beyond than the rating say around load: 352kva... Than how can we solve this problem without deducting the load.
HT motors are generally connected in star, what will be the effect if we connect HT motor in Delta?
6 Answers Equate, Ion Exchange,
what would happen nif we increase or decrease the capacitor of a flood light.
what is cogging and crawling
20 Answers ABB, Ashok Leyland, Bharat Bijlee, BMRCL, MN Dastur, Siemens,
11 kV line deraction check by an Engineer.
What is the relation between the Peripheral speed(N) , no.of poles(P) and diameter(D) of a cylindrical rotor alternator ?
If load current is 70amps or 50amps what range of CT to install for ampere metering
whta is difference between contactor and breaker.
hi friends i m from electrical branch and seeking for tech. + apti. both papers of hpcl plz get it available as soon as possible
0 Answers Engineers India, Engineers India Limited,
SUPPOSE A CIRCUIT BREAKER HAS TRIPPED THE THE LINE WHEN A FAULT OCCUR ON IT.NOW WHEN THE FAULT HAS BEEN CLEARED, HOW THE CIRCUIT BREAKER WILL CLOSE AUTOMATICALLY NOT MANUALLY.
6 Answers Bureau of Energy Efficiency, DVC,
OHMS Law is only applicable for ac or dc or both circuiT?.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)