Why the substation measure in KV but not in the power ratings of transformer.
Answers were Sorted based on User's Feedback
Answer / j.prakash
Transformer is static device there is no any rotating part
so there is no any friction losses, only iron loss and cu
loss in transformer, iron loss depend upon the voltage and
cu loss depend upon the current, there in no any loss which
depend upon power factor,so rating of transformer only in
kva.SO NOT IN KW..
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / narendra
the transformer rating in kva.the substaion step down or
step up the voltage the current will be constant
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sunil bhuarya
above answer is correct if we talk about transformer, but as question is why s/s in kv....?? transmission capacity of incoming feeder is named as 400Kv, 220KV 132KV and so on...
for ex. in 220KV/132KV/33KV s/s there will be at least one /two 220Kv line and 132KV outgoing feeders that may be depend on the requirement..
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / k.prakashchandra
The structure and insulation levels of materials used are
designed on the basis of system voltage which remains unaltered.
| Is This Answer Correct ? | 0 Yes | 1 No |
How much earthing frequency is capable?
What is process of anneling transformer core
What is the formula for calculating Transformer Losses & Efficiency. I want to compare the Transformer efficiency at different loading condition.
6 Answers Rays Power Experts, Techser,
how to calculate a cable size while load is given in amp or kw and length is also define.?
during positive and negative half cycle of ac supply what happenes in the load?
Does the hysteresis loss is due to retentivity property of the material? or it is due to reluctance property?
Any formula to calculate neutral current in 3 phase 4 wire system
what will be the min and max voltage flow from neutral to earth?
in alternator how we can give power to rotor ? its power is AC or DC ?
If R and Y terminals are short circuited,then power will cut. we all know that power cannot be stored.what will happen to already generated power at power station?
What is real time power factor control panel(RTPFC)?
For 415v,3phase,22kw rating of motor how to calculate MCCB rating
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)