Why the substation measure in KV but not in the power ratings of transformer.
Answers were Sorted based on User's Feedback
Answer / j.prakash
Transformer is static device there is no any rotating part
so there is no any friction losses, only iron loss and cu
loss in transformer, iron loss depend upon the voltage and
cu loss depend upon the current, there in no any loss which
depend upon power factor,so rating of transformer only in
kva.SO NOT IN KW..
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / narendra
the transformer rating in kva.the substaion step down or
step up the voltage the current will be constant
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sunil bhuarya
above answer is correct if we talk about transformer, but as question is why s/s in kv....?? transmission capacity of incoming feeder is named as 400Kv, 220KV 132KV and so on...
for ex. in 220KV/132KV/33KV s/s there will be at least one /two 220Kv line and 132KV outgoing feeders that may be depend on the requirement..
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / k.prakashchandra
The structure and insulation levels of materials used are
designed on the basis of system voltage which remains unaltered.
| Is This Answer Correct ? | 0 Yes | 1 No |
What is effect of power factor on change in voltage
13 Answers APNPDCL, apspdcl, My Home Industries,
define IDMT relay?
15 Answers APGenco, Bhel, L&T, Shriram Finance,
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating
what is cogging and crawling
Why transformer used in UPS??
Here iam a question with SYNCHRONIZATION PANNEL related issue, as i want to design a SYNC.pannel board iam giving the 2 nos of 1MVA Generators to sync pannel , then what wil be the out put of the sync pannel, whether it wil be one cable coems from the sync panel or two cables.. as iam using two transformers to meet my load demand, so pls clear me whether two cables comes from sync panel to connect to transformers or only one cable
What is difference between Sample test and Routine test in safety standard?
0 Answers Chicony Electronics,
is it value of power factor is more than unit. whats effects in the source supply
How do the synchronizing lamps indicate the correctness of phase sequence between existing and incoming alternators?
what is diversity factor ? plzzzzzz describe me
In what cases (circumstances)we should apply P controller, PD controller, PI controller & PID controller ?
Briefly describe three methods that are usually used by electricity suppliers to control voltage levels?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)