Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why the substation measure in KV but not in the power ratings of transformer.

Answers were Sorted based on User's Feedback



Why the substation measure in KV but not in the power ratings of transformer...

Answer / j.prakash

Transformer is static device there is no any rotating part
so there is no any friction losses, only iron loss and cu
loss in transformer, iron loss depend upon the voltage and
cu loss depend upon the current, there in no any loss which
depend upon power factor,so rating of transformer only in
kva.SO NOT IN KW..

Is This Answer Correct ?    6 Yes 2 No

Why the substation measure in KV but not in the power ratings of transformer...

Answer / narendra

the transformer rating in kva.the substaion step down or
step up the voltage the current will be constant

Is This Answer Correct ?    0 Yes 0 No

Why the substation measure in KV but not in the power ratings of transformer...

Answer / sunil bhuarya

above answer is correct if we talk about transformer, but as question is why s/s in kv....?? transmission capacity of incoming feeder is named as 400Kv, 220KV 132KV and so on...
for ex. in 220KV/132KV/33KV s/s there will be at least one /two 220Kv line and 132KV outgoing feeders that may be depend on the requirement..

Is This Answer Correct ?    0 Yes 1 No

Why the substation measure in KV but not in the power ratings of transformer...

Answer / k.prakashchandra

The structure and insulation levels of materials used are
designed on the basis of system voltage which remains unaltered.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

How the power factor is more in high speed machines

1 Answers  


what is the lightning arrester rating for 3.3kv system voltage

1 Answers  


1.wat is the negative slip region in the motor?

1 Answers  


i m in need of current rating chart of heavy duty pvc/xlpe, cu/al cables. can somebody provide me? if yes, plz send me at ashish_patel111@yahoo.com

0 Answers  


I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current 36 A,but wenn i put load after 2 hours the current increase more than 156 A. Can anybode tell me waht is the Problem?

4 Answers   ABB,


Why we are going for converter transformers for DC drives application instead of distribution transformer?

0 Answers  


what is the difference between line & phase current in star delta connection motor?

2 Answers  


give me atleast four differences between circuit and network

0 Answers  


What is the Ohms low calculation

2 Answers  


MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III

1 Answers  


If we need 4c× 50mm sq cable but it's not available so we can pull 4c×25mm sq two cables?

0 Answers  


From the point of view of accuracy in the Measurement of Electrical energy should we select a potential transformer or a capacitor voltage transformers?.Kindly support your reply with reason and justification.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)