Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to measure corona loss in a transmission line?(Plz ans
only if u know the exact answer)

Answers were Sorted based on User's Feedback



How to measure corona loss in a transmission line?(Plz ans only if u know the exact answer)..

Answer / roysayan01

well let me answer my own question-

I'll let you know,measuring Corona loss is no child's
play.Even if you are well equipped in the field of power
transmission, errors would creep in.

The expression for corona loss is given by

Peek's equation

Pcl = (244/q)*(f+25)*(Sqrt(r/D))*(Vph -Vd0)^2 * 10^ -5
Kw/Kw/phase
You think that's complicated? There is more to come.

In the above expression r is the radius of the wire in
meters and D is the effective distance between the wires in
meters,f is the frequency of transmission voltage,Vph is the
voltage to neutral or the phase voltage and Vdo is the
Disruptive critical voltage.

q = Air density factor which is given by expression
((273)/760)* p/(273+t)

All the calculations for q are done by converting
temperature into Kelvin scale
273 K in the Standard temperature and 760 mm of mercury is
the standard pressure and they are taken into consideration
in the above expression.
p is the atmospheric pressure when measurement is to be done
and t is the temperature in degree celcius at that time

The expression reduces to q = 0.359p/(273+t)
Hold this tight we'll get back to it later on

Now we need only Vdo or the disruptive critical voltage(The
voltage at which corona effect occurs) to calculate the
corona loss

Vdo=go x m x q x rx ln(D/r)
go is the breakdown strength of air.It's about 30KV at
normal temperature.
m is the irregularity or roughness factor of the condutor
which is a given thing.
q is Air density factor which as discussed above
and D and r are the effcetive distance between conductors
and the conductor radius.

No we have all the required things to measure corona loss.
Putting all the values in right place in the Peek's
equation, we get the corona loss.

hope i explained the whole process vividly.

Is This Answer Correct ?    7 Yes 1 No

How to measure corona loss in a transmission line?(Plz ans only if u know the exact answer)..

Answer / raghavendran.r

thanx for that detailed explanation, but kindly clarify how
to calculate the power loss due to corona.You have arrived
at Vdo the disruptive voltage where corona begins.but how to arrive at the total power loss due to corona and i think
thats the question that you have also asked.

Is This Answer Correct ?    1 Yes 1 No

How to measure corona loss in a transmission line?(Plz ans only if u know the exact answer)..

Answer / remya reghnath

The measurements were performed using a coaxial measurement
arrangement with different bundle and conductor types. The
effects of conductor and bundle type, temperature, applied
voltage and hoar frost thickness on corona losses were
investigated. A two-conductor bundle had corona losses about
2.5...5 times higher than a three-conductor bundle.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

The initial current is very large at the time of starting for almost all DC motors. SO WE USE STARTER FOR A SAFE STARTING but at our homes we don’t see any starters in our coolers, motors.WHY DON’T WE NEED STARTERS FOR THESE APPLIANCES?

1 Answers  


why we have to do tan delta test of the transformer oil???

5 Answers  


what is meant by class 1 E in electrical power supply?

0 Answers  


In transformers Which type of connection is preferred for harmonics to be minimum. primary : secondary star without neutral:open delta star with neutral :open delta star without neutral: delta star with neutral : delta explain why

1 Answers   Genco,


help!!!! i bought a new house 2 yrs ago,ive just had 2 new lights fitted,when i boil the kettle,maybe 2 times in succession the safety light switch trips out,it dosnt do it straight away but it seems to do it when the kettle boils!!!!! sounds very odd to me

2 Answers  


why generator is star connected ?

3 Answers   Voltech,


Define the "All - Day Efficiency" of a Transformer

1 Answers   Transco,


Why efficiency of generator is higher than motor at a particular load?

0 Answers  


Why we use ups battery and dsdb battery in thermal power plant

0 Answers   MDeC,


what is the use of Reactive power

2 Answers  


if sf6 gas low in gis what will happen

0 Answers  


1) why a dg set shows variation of power factor and load when synchronised with other dgs? 2)Why the load sharing is not become equal in all dgs?. 3)When a dg set will not run on auto start?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)