Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to measure corona loss in a transmission line?(Plz ans
only if u know the exact answer)

Answers were Sorted based on User's Feedback



How to measure corona loss in a transmission line?(Plz ans only if u know the exact answer)..

Answer / roysayan01

well let me answer my own question-

I'll let you know,measuring Corona loss is no child's
play.Even if you are well equipped in the field of power
transmission, errors would creep in.

The expression for corona loss is given by

Peek's equation

Pcl = (244/q)*(f+25)*(Sqrt(r/D))*(Vph -Vd0)^2 * 10^ -5
Kw/Kw/phase
You think that's complicated? There is more to come.

In the above expression r is the radius of the wire in
meters and D is the effective distance between the wires in
meters,f is the frequency of transmission voltage,Vph is the
voltage to neutral or the phase voltage and Vdo is the
Disruptive critical voltage.

q = Air density factor which is given by expression
((273)/760)* p/(273+t)

All the calculations for q are done by converting
temperature into Kelvin scale
273 K in the Standard temperature and 760 mm of mercury is
the standard pressure and they are taken into consideration
in the above expression.
p is the atmospheric pressure when measurement is to be done
and t is the temperature in degree celcius at that time

The expression reduces to q = 0.359p/(273+t)
Hold this tight we'll get back to it later on

Now we need only Vdo or the disruptive critical voltage(The
voltage at which corona effect occurs) to calculate the
corona loss

Vdo=go x m x q x rx ln(D/r)
go is the breakdown strength of air.It's about 30KV at
normal temperature.
m is the irregularity or roughness factor of the condutor
which is a given thing.
q is Air density factor which as discussed above
and D and r are the effcetive distance between conductors
and the conductor radius.

No we have all the required things to measure corona loss.
Putting all the values in right place in the Peek's
equation, we get the corona loss.

hope i explained the whole process vividly.

Is This Answer Correct ?    7 Yes 1 No

How to measure corona loss in a transmission line?(Plz ans only if u know the exact answer)..

Answer / raghavendran.r

thanx for that detailed explanation, but kindly clarify how
to calculate the power loss due to corona.You have arrived
at Vdo the disruptive voltage where corona begins.but how to arrive at the total power loss due to corona and i think
thats the question that you have also asked.

Is This Answer Correct ?    1 Yes 1 No

How to measure corona loss in a transmission line?(Plz ans only if u know the exact answer)..

Answer / remya reghnath

The measurements were performed using a coaxial measurement
arrangement with different bundle and conductor types. The
effects of conductor and bundle type, temperature, applied
voltage and hoar frost thickness on corona losses were
investigated. A two-conductor bundle had corona losses about
2.5...5 times higher than a three-conductor bundle.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.66 how can we maintane it? how can we balance our load?

4 Answers  


Frequency of rotor emf in induction motor is around A same as stator frequency B 50% C 5 % or below D 30%

1 Answers  


how we control automatic generator i'e with to supply (main supply and local generator) when the main supply was break to supply the local supply automatically to begin supplying power.I now this control circuit is the combination of contactor time delay contactor switch and overload relay .but my question is how we combine those component thank you

0 Answers  


15 suspects are rounded by the police and questioned about a bank robbery. Only one of them is guilty. The suspects are made to stand in a line and each person declares that the person next to him on his right is guilty. The rightmost person is not questioned. Which of the following possibilities are true? A. All the suspects are lying. B. The leftmost suspect is guilty. B only

2 Answers   TCS,


What is primary distribution and secondary distribution of ac power?

3 Answers  


full form of flry b

0 Answers   KPIT,


why transformer is rated in kva instead of kw?

1 Answers  


respetsed sir, i have applied for section engg and juniour engg for both chennai and tiruvunabthapur boards for electrical deportments . can u suggest what books i have to follow and and also from which sections they r going ask (i mean weightage and what topics i have to cover) for both se and je for both chennai and tiruvunanthapur boards.......

1 Answers  


When a square wave is applied to primary of a transformer then what will be output wave form of secondary ?

0 Answers  


what is a difference b/w earthing & neutral?

5 Answers   ABB, KEC, Sterlite,


how to calculate fault level?

0 Answers   Mylan,


An alternator is started without excitation then how much voltage it will produced at strating at full rpm??

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)