I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency
75%(star delta connection)Motor. How to calculate line
current & Phase current (1) Star connection (2) delta
Connection
Answers were Sorted based on User's Feedback
Answer / s c budhiraja
(1) First for star connections:line
current=1000/.75*1.73*.75*440=1.75 A for both line &
phase.
(2) For delta connections; Line current=1.75A
Phase current=1.75/1.73=1A
Note: There no use of Motor efficiency here.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / michael
NOTE : YOU NEED MOTOR EFFICIENCY
BECAUSE IF THERE IS A RATING GIVEN
IN TERMS OF KW. IT IS ALWAYS THE
OUTPUT POWER OF THE MOTOR..
SO WEE NEED TO CONVERT IT TO
INPUT POWER IN ORDER TO COMPUTE THE
CURRENT.
Is This Answer Correct ? | 4 Yes | 0 No |
What is I to C?
what is ground fault current? is there any current flow takes place through ground? is it possible? if it's possible whether it affect human beings on earth near the fault or not?
why we dont store the ac power in battery?
HT and LT cables can be laid on same cable tray
Please help me.What are the difference between two wire, 3wire, and 4 wire in electric meter?
what is the relation between KVAR,KVA,KW?why we are mentioning capcitor rating in kvar?what is meant by arcing horn and horn gap in transformer?what is equipotential wire?
what happen when we add mentos in cold drink?& why?
Why only sinusoidal ac voltages are generated?why not triangular or sawtooth?
Q2). When 3 dice are simultaneously thrown, which of the following would be obtained? (a) Result 1: “A 5, a 3 and a 6” (b) Result 2:” A 5 three times” (c) Result 3:”A 5 twice and a 3” (d) All three results are equally likely. (Musigma Question)
I want single line diagram for AMF & DG syncronizing panel
CAN ANYBODY PL TELL ME WAT FACTORS CAN CAUSE UNDERVOLTAGE ON A BUS??? PL LIST ALL THE REASONS WITH SOME EXPLAINATION
What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?