How to calculate meter constant in HT yard pls give me
example for this issue
Answer / mohamed ali.m
Hi,
This is Formula ,
PT ratiox CT ration X dial Constant/ Meter PT raioxCT ratio
example ,
100x60x1/1x1 = 6000
example
Final Reading Kwh - 2342.4 , Intial reading Kwh - 2339.5
so Consum 2.9x 6000 = 17400 units Consumed
good Question
| Is This Answer Correct ? | 9 Yes | 0 No |
what is the difference between equipment earth and system earth.
state types of reflectors in illumination engg. ???????
When the power Factor (p.f)is lead then how the Voltage can rises?
if 20 hp motor starts directly delta connection.motor what will be the effect.
hoW to select a CT?
How does frequency affect KVA rating of a transformer? If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz frequency then how will its KVA rating change? a-increase b-decrease c-remains same Also explain why do u think like that.
what is the effect of constant power factor to the voltage regulation
In cable sizing calculation (determining the max route length of cable) why we choose the shortest length between cable length of full load current Iflc & starting current Istart?
why do we not use equivalent voltage source in negative sequence equivalent ckt.
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
along with technical test papers
How to calculate VA rating for CT or PT or Control Transformer?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)