how can we find a burden of potential transformer? what
does it effects? how can we calculate rated load of it?
Answer Posted / tuktuk
Dear Mr.Raghavendran,
Thank you for your answer, I have the same problem but after reading your answer I still have some concerns.
I am really confused. In this case, we do not know the rated burden of the VT. Now we have to calculate the total burden and then selecte the rated value from IEC standards.
__Ztotal, which you mentioned above, is in Ohm or VA?
__Zsec and Zrelay we can get the value from manufacturer but Zlead, is it calculated by this formula: Zlead= (p*L)/S
(where: p is specific resistivity of copper in ohm.mm^2/m; L is length of lead between the PT secondary and the relay in meter; S is the section of lead in sqmm)? Is this true?
__I dont know how can we get secondary current Isec? (I guess Isec=Usec/Zt, isn't it?)
__And Burden in VA = Zt*Isec. As Ohm law, we have P=VI=RI^2=U^2/R, I do not understand the formula that you used to calculate Burden of VT in VA
Hope that you could help me to solve this stuck in my head.
Thank you.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
PIU how does work?
Explain about Leakage Test.
If there is major % of Voltage harmonics in the system, how can it be control or reduced?
state basic meaning of 'INDUSTIAL AUTOMATION'?
how can we say that stator magnetic field rotates with synchronous speed?can we derive?
What is the formula to calculate the no load current of a single & three phase induction motor
For refrigerators the motor current is raised beyond its rating on both conditions when the voltage of the system is more(say 270v) than the rated voltage(220v) as well as when the voltage of system is less(say 160v) than normal voltageof 220v, why explain?
what is the prosses for getting of 33kv licence (i have completed my engineering degree & working in 33kv substation for contract basis )????
How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts
Explain Active power,reactive power,how its related to each other , & inductive ,capacitive.
what is the standard values(Megger test) of resistances between L&N,L&E and N&E for a system on IEE regulations?
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?
What is the difference between hot and cold loop testing?
how we decide scurt (disc) of insulator with respect to kv rating
what is earth fault relay 64T, why it is used in main Incomer and neutral CT of Transformer.