tan delta test of current transformer.
Answers were Sorted based on User's Feedback
Answer / raghavendran
Tan Delta test is performed on transformers to test the
insulation strength of its Bushings,Oil,Winding - winding
insulation Strength.It is also called as dielectric
Dissipation factor.it is measured by applying Voltage across
the Insulation and the intensity of the charging current say
(Ic) and resistive current (Ir).the value of Ir should be
low and thus denoting that the insulation is good.
Is This Answer Correct ? | 36 Yes | 4 No |
Answer / praveen
Tan Delta, also called Loss Angle or Dissipation Factor testing, is a diagnostic method of testing cables to determine the quality of the cable insulation.In a perfect capacitor, the voltage and current are phase shifted 90 degrees and the current through the insulation is capacitive. If there are impurities in the insulation the resistance of the insulation decreases, resulting in an increase in resistive current through the insulation. It is no longer a perfect capacitor. The current and voltage will no longer be shifted 90 degrees. It will be something less than 90 degrees. The extent to which the phase shift is less than 90 degrees is indicative of the level of insulation contamination, hence quality/reliability. This “Loss Angle” is measured and analyzed.
Is This Answer Correct ? | 10 Yes | 2 No |
What is the difference between analogue electronics and digital electronics?
in house wiring when two wires are same colour coding and there is no any connection one end how to find which wire is earthing wire
why the transformer has no starter
how does a current carrying conductor posess a magnetic field. what is the reason for the production of electro magnetic field around the conductor
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
What is the meaning of STAR POINT? Why this important in CT and VT?
Can without battery on line UPS,off line UPS or Invertor works please brief.
What determines the thermal loading on the motor?
sigal phase supply is 230 v ac two phase supply is 415 v ac then why three phase supply having supply is 415 v ac why not 690v ac
could i arrange a faulty and healthey battery bank togather in parallel , if your ans is not then why?
what is the cost of a analog tachometer, for lab purpose/
Instead of single phase(220), if apply Phase to phase supply (eg: for lighting fixture). what will be the power formula? what will be the volt and current value? please explain me with some example.