tan delta test of current transformer.
Answers were Sorted based on User's Feedback
Answer / raghavendran
Tan Delta test is performed on transformers to test the
insulation strength of its Bushings,Oil,Winding - winding
insulation Strength.It is also called as dielectric
Dissipation factor.it is measured by applying Voltage across
the Insulation and the intensity of the charging current say
(Ic) and resistive current (Ir).the value of Ir should be
low and thus denoting that the insulation is good.
| Is This Answer Correct ? | 36 Yes | 4 No |
Answer / praveen
Tan Delta, also called Loss Angle or Dissipation Factor testing, is a diagnostic method of testing cables to determine the quality of the cable insulation.In a perfect capacitor, the voltage and current are phase shifted 90 degrees and the current through the insulation is capacitive. If there are impurities in the insulation the resistance of the insulation decreases, resulting in an increase in resistive current through the insulation. It is no longer a perfect capacitor. The current and voltage will no longer be shifted 90 degrees. It will be something less than 90 degrees. The extent to which the phase shift is less than 90 degrees is indicative of the level of insulation contamination, hence quality/reliability. This “Loss Angle” is measured and analyzed.
| Is This Answer Correct ? | 10 Yes | 2 No |
I decided to provide a 11KV / 440V Xformer in my Substaion. What are the protection required for that?
what is the function of 1 phase preventer?
Is the theorem applicable to ac sources?
what is the criteria for selection of conductor used for ehv ac electrical dischrge
0 Answers National Productivity Council,
Our Company's Contract Demand is 110 kVA. We use 12 Capacitors each of 12.5 kVAr Capacity to maintain Power Factor of 0.99. So, what steps should we take so that our Contract demand does not exceed 110 kVA?
why we use CVT (capacitive voltage transformer)in switch yard?
What is the difference between electronic regulator and ordinary rheostat regulator for fans?
WHY HVDC?
How to calculate Grid rotor resistance(GRR) losses in slip ring induction motor?
What do you mean by reach and reach the point of the relay?
The screw thread commonly used for transmission of motion is one of the following types of threads
in 132 kv transformer , in which range of transformer oil bdv required ? if it has around 50-55 , then how it was insulated the winding ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)