Answer / m m chotrani
Yes we can measure interface level by purge method.you can
use two purges (sensors of ss pipe generally 1/4"NB).Now
for interface measurement two liquids of different
densities should be there. suppose the interphase takes
place between 300 and 450 mm height from the bottom of the
tank.now the interface be 50%. height difference (probe
distance is 150 mm. multiply 150 withe density of 1st
liquid say 0.8 gm/cc.which will be 120mm. and multiply 150
with the density of another liquid with the density say 1.2
gm/cc which is 180 mm.So your transmitter range is 120-180
mm of water column. calibrate the transmitter for this
range and connect both the probes to HP and LP connections
of transmitters
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ikarous
No,its not possible
you can use the level displacement transmitter which acts
according to buoyancy law
Is This Answer Correct ? | 2 Yes | 3 No |
What is the load line in control valve?
What is Modbus communication
What are the cable come out from the paddle type flow sensor.and how is further connections
how to calibrate TT transmitter
Can anyone provide me the details of GAIL test paper?What is the format and what type of questions will be there? my id-princegnb@gmail.com
how many type of control valve?
If we increase D what will be the controller action?
what is the difference between 2 wire and 3 wire RTD- application wise,cost effectivity?
Please can anybody help for control valve sizing step by step procedure?
what deference between panel earth and systemearth
WHAT IS A CALLIBRATION? WHAT IS MEEAN BY LOOP CHECKING INCLUDES PRESURE, THERMOCOUPLE,TT,DT?
what is the differnce betweeen hart and smart tx