how we can measure the interface level?is it possible to
measure interface level with dp or pressure transmitter?

Answers were Sorted based on User's Feedback



how we can measure the interface level?is it possible to measure interface level with dp or pressu..

Answer / m m chotrani

Yes we can measure interface level by purge method.you can
use two purges (sensors of ss pipe generally 1/4"NB).Now
for interface measurement two liquids of different
densities should be there. suppose the interphase takes
place between 300 and 450 mm height from the bottom of the
tank.now the interface be 50%. height difference (probe
distance is 150 mm. multiply 150 withe density of 1st
liquid say 0.8 gm/cc.which will be 120mm. and multiply 150
with the density of another liquid with the density say 1.2
gm/cc which is 180 mm.So your transmitter range is 120-180
mm of water column. calibrate the transmitter for this
range and connect both the probes to HP and LP connections
of transmitters

Is This Answer Correct ?    1 Yes 0 No

how we can measure the interface level?is it possible to measure interface level with dp or pressu..

Answer / ikarous

No,its not possible
you can use the level displacement transmitter which acts
according to buoyancy law

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Instrumentation Interview Questions

What is PID tunning

2 Answers   EID Parry, MFL,


PLS TELL ME THE FUNCTION OR PRINCIPLE OF CREEP RELEIF VALVE..

3 Answers  


What is the maximum operative of Drive ?

2 Answers   Reddy Labs,


why r using 250 resistances

6 Answers   Sabic, Samsung,


how to replace the smart transmitter software

1 Answers   L&T,


please send the sample qustion paper for iocl written test ..

0 Answers   IOCL,


what effects a surging can produce in the compressor

0 Answers   Nemat,


What is the difference between Analytical instruments and other instruments?

7 Answers   Schenck,


what is the process to make control schematic ?

0 Answers  


how level can be measured in open tank with reference to pressure

1 Answers   Atul, INOX,


I have a MRE200 amplifier for controlling a mitsubishi servo motor, I would like to know how many pulses are required to rotate the servo motor by 1 degree and what must be the pulse width

1 Answers   Essar,


Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.pls help me

1 Answers   Worley Parsons,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)