how to check the stabilty test for generator differential
protection
Answer / raghavendran
Checking of the pickup and dropout value
When checking the pickup value, the analogue input signals
of the single phase alternating test current have to be fed
to the relay via terminals.When testing the pickup value,
the alternating test current must first be lower than the
set pickup value.
Then the current will be increased until the relay picks up.
The value that can be read from the ammeter may not deviate
by more than ± 2.5% of the setting value. The tripping
values for the other current inputs should be checked
accordingly.
Function test
Disconnect all leads for adjusting the interposing C.T.s and
perform the following function test:
Load the generator with minimum 50% load. Assure that the
tripping of the generator C.B. does not cause un-wanted
damages (blackout).
To operate the differential relay use a shorting link
between one of the phase measuring sockets
and GND, e.g. connect Line to GND. The relay should trip
immediately. If no trip occurs, make sure
that the load current exceeds the set value.
Is This Answer Correct ? | 0 Yes | 1 No |
Explain RYB?
why we use the 100% and 95% stator earth fault protection for the synchronus generator ?
0 Answers Operational Energy Group,
what happen if transformer neutral not earth
What is ST and specify its range of voltage.
in transformers for ex. 100mva and 400kv the secondary current is about 420 amps but for selection of bushing the capacity of selected bushing is 2000A why there is such big difference ?
why we calculate only 11kv 33kv and 132kv ... why not 10kv 20kv 45kv?
what does the regenerative braking mean?and how it used for Dc motor? thanks.
which gas is cost wise high?
What is the knee point of voltage of CT?
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
What is main cause of cable's terminal point burned in Lug on high temperature although lug and cable selection is ok as per stantard and also tightness is ok as per situation. so please take in deep and tell correct answer thanku.
After taking shutdown of 11kv feeder, if you see 5kv by phasing stick in the cable side, is it possible to close earth switch in cable.