how to check the stabilty test for generator differential
protection
Answer / raghavendran
Checking of the pickup and dropout value
When checking the pickup value, the analogue input signals
of the single phase alternating test current have to be fed
to the relay via terminals.When testing the pickup value,
the alternating test current must first be lower than the
set pickup value.
Then the current will be increased until the relay picks up.
The value that can be read from the ammeter may not deviate
by more than ± 2.5% of the setting value. The tripping
values for the other current inputs should be checked
accordingly.
Function test
Disconnect all leads for adjusting the interposing C.T.s and
perform the following function test:
Load the generator with minimum 50% load. Assure that the
tripping of the generator C.B. does not cause un-wanted
damages (blackout).
To operate the differential relay use a shorting link
between one of the phase measuring sockets
and GND, e.g. connect Line to GND. The relay should trip
immediately. If no trip occurs, make sure
that the load current exceeds the set value.
Is This Answer Correct ? | 0 Yes | 1 No |
is there any pottential in neautral?
How can we calculate single phase load into three phase load
how to read AWG n how to convert AWG reading into mm?
give me list of material for wiring of 20hp motor?
motor work in hat principle generator work in what principle transformer work in what principle pls explain with details or answered to ramadoss.sepc@gmail.com
How can we calculate the transformer rating if the load calculated is 1000KW (11Kv Supply)?
if field current decreases how can the speed increase in the unloaded dc series motor
if we are using ACB in a panel the how much clearance do we need in panel room.
Why in Hv transmission line as we see there are generally 6 or more than 4 conductor wires are used instead of 4 i.e. 3 for phase and 1 for neutral wire?????
Generally we denote power in 'p',voltage in 'v'but why can't we denote current in 'c' instead of I.
Is there any capacitor in 3-phase IM?why,xplain.
What will be the excat cable specification in Sq MM...please find the details below.... Induction Motor HP:55 Amps:70(starting Amps),45(Running Amps). Volts:415