Hello friends i am facing one problem in lighting panel.
Frequently neutral link near to MCCB is burning(firing. What
may be the reason for this one. Please answer me.
Answers were Sorted based on User's Feedback
Answer / sunil guru
the current rating is greater than the MCCB rating. so go for
higher current rating...
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / m v v s n murthy
Generally, we will distribute our 1 phase loads equally in 3
phases to get the balanced load and the circuit becomes star
connected. In star connection, there will be no current in
neutral line if the load is balanced.
In the lighting loads also we have to distribute equally in
3 phases. If not, current will increased in neutral.
In your case you did not devide the lighting load to get
balanced star connection, and also the neutral link in your
MCCB under size to carry unbalanced neutral current. And
also there may be loose connection at neutral link.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / sachin
Dear friend ,
First measure the current flowing thro MCCB .If it is MCCB
then it must have protective system . Set it as per max
current.measure the neutral current at full load. measure
neutal to earth voltage . most possible reasons are
1] Neutral link is undersized or
2] Loose connections
3] Neutral is not properly earthed .
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / anirudha
the mccb is burning because the rating for the current for
which it is selected may not be proper
Is This Answer Correct ? | 0 Yes | 1 No |
Write down the design procedure of commutaj.
Questions :- HR- Q.1 about yourself & family background ? Q.2 Why u choose Power sector as ur carrier starting not any other sector ?? Q. 3 What think abt NTPC ? Techincal Questions:- Q.1 about Vocational Training……What u did , see the main equipments….etc Q.2 Why a transformer Noise during its running condition ? Q.3 about transformer oil material & Test name for the measurement of its dielectric strength & wht will u do if its dielectric strength goes low ? ……..some discussion type ? Q.4 What is relation between transmission lines & Communication lines ? Q.5 Which Machine u will prefer to use at a place where flammable gases are coming out & why ? Q.6 how fault in an electric system is detected & hw protection of equipments is done ? Q.7 Why we didn’t feel electric shock in an electric train ?? Q.8 Anything u want to ask from us ??
44 Answers Akona Engineering, Bhel, BSES, Cranex, DRDO, JCB, NTPC,
How to desaturate a saturated CT of PS Class?
How to megger test 11 kV cable and the acceptance IR value
diff between UPS and inverter?
why we use carbon brush in exciter&genrator?
Explain Clearly Pahase and Neutral?
how to calculate the magnetizing current of ct ( 800A/1A) for Relay 64
If anyone would like to know or practice for FEWA papers contact me on mohamedrashad2@hotmail.com Just completed the supervisor exam in April 2021
what are doing the duall connetion in tree phase 10hp or etc motor with circuit diagram
what is the working process of over & under voltage relay.
What happens to voltage when current is zero?