Answer / sunil guru
the current rating is greater than the MCCB rating. so go for
higher current rating...
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / m v v s n murthy
Generally, we will distribute our 1 phase loads equally in 3
phases to get the balanced load and the circuit becomes star
connected. In star connection, there will be no current in
neutral line if the load is balanced.
In the lighting loads also we have to distribute equally in
3 phases. If not, current will increased in neutral.
In your case you did not devide the lighting load to get
balanced star connection, and also the neutral link in your
MCCB under size to carry unbalanced neutral current. And
also there may be loose connection at neutral link.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / sachin
Dear friend ,
First measure the current flowing thro MCCB .If it is MCCB
then it must have protective system . Set it as per max
current.measure the neutral current at full load. measure
neutal to earth voltage . most possible reasons are
1] Neutral link is undersized or
2] Loose connections
3] Neutral is not properly earthed .
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / anirudha
the mccb is burning because the rating for the current for
which it is selected may not be proper
| Is This Answer Correct ? | 0 Yes | 1 No |
when current lags behind voltage how does it affect the circuit.In other words what is the significance of lagging current?
what is the circutor?why we use it ?
Name different types of fault and which instrument is used to measures earth,short,open cicuit fault?
6 Answers NTPC, Vijai Electricals,
it is used to measure the potial difference between two point?
Scott connection is used for A 3-phase to 2-phase conversion B to achieve higher effciency C to save copper D to reduce harmonics
magnetizer priciple
what is power factor? how can we correction the power factor if this is high or low? If anyone know please please send the answer on my email id ( kumarkirshan@in.com )
how we protect the motor & what are the components required for that ?
please tell me the all the spcications of the 100MW 11KV HYDEL POWER PLANT SPECICATIONS
pls,send the previous year written test questions.
Why the CT Secondary is rated as 5A generally?
What is the maximum and minimum rating of UPS?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)