what is the formula to calculate kva genset required for a
given load in kw.
Answers were Sorted based on User's Feedback
Kva Required is = KW/0.8( Power factor )
& as the DG set is prefered to run at 80% load of the total
capacity then the Rated capacity is KVA/0.8
If the load is 100 KW rhen KVa is 100/0.8 = 125 KVa & the
rated kva is 125/0.8 = 156.25 KVA say 160 kva D.G set is
required.
| Is This Answer Correct ? | 34 Yes | 6 No |
Answer / vaibhav kr. pathak (ongc,hazir
Normaly relation between kVA and kW can be described as:
For 1phase system->kW=kVA X power factor.
For 3phase system->kW=3^(1/2)*V*I*power factor (V&I are
line voltage and current respectively)
| Is This Answer Correct ? | 3 Yes | 0 No |
Why MCCB is Getting tripped sometimes when there is no load in the Midnight ?
WHY CAPACITOR IS NOT USED FOR THREE PHASE MOTORS DURING STARTING
sir,in our plant we r using SATEC PM172E power reading meeters in HT panel side it is monitoring the MB data smart viewer(sever).but last one week we did not get readings inthe server only available in meeter.tell me how communicate meter and server. and also what steps we take for checking.
Why dose an electric meter record KVA when there is no load on a 500 KVA transformer
1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for grounding? 3)What is the difference between ELCB &RCCB? 4)Why we use iron core in transformer insted of wooden core? 5)what is the principle of excitation? 6)Why we test the core balance test for transformer? 7)what is creepage?What is the creepage length for insulators at different voltages? 8)How much type of relays used for differential protection of generator,transformer & busbar protection?
hey guys i recently saw a long transmission line in which a sort of balloons in red and white color were hanging at each section.do u have any idea why are they kept for?
110 KW MOTER DOL STATER 240SQ.MM CABLE MOTER AND STARTER DISTANCE IS 110 METER WHAT IS VOTAGE IN MOTER END AND SYSTEM VOTAGE IS 415 V HOW I CAN CALCULTE
What is industrial plc
Name two types of electrical analogous for mechanical system.
a wire in which bulb is connected there is two terminal when one terminal is connected to phase than why the value of current shock in nutral terminal is max. or large??
how can calculate resistance box for 15 kw, 6 pole, RV-230, RA-42 motor
What is contract demand in solar system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)