Why OLTC(On Load Tap Changing)transformer is not recomended
for improving voltage instability?
Answers were Sorted based on User's Feedback
Answer / iamdon
Voltage instability is due to following reasons:
1)Gradual increse in load.
2)Loss of generating unit or heavily loaded line
3)Poor cordination amoung control action to avert the
situation etc.
In all the cases the system is insufficient to cater the
reactive power requirement of the load.It leads to the
reduction in voltage at load end.
OLTC transformer increases the voltage level at load side
so Q requirement of load increases.The system is already
running short of Q, so it is not possible to supply this
incresed Q by system.This leads to more voltage dip at
load.In this way, instead of stabilizing the voltage, OLTC
transformer aggerevate the voltage instability.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 5 Yes | 0 No |
oltc worked in step not in pid mode only avr worked in pid mode
| Is This Answer Correct ? | 2 Yes | 1 No |
how to Select its CORE in electrical cables based on its applications? or Application of various types of electrical cable based on it CORE?
Why do power lines not short out when they fall into water?
what is the function of supervison relay?Draw its wiring diagram.
2 Answers IBM, R.R. ISPAT LIMITED,
How to design grid earthing
What will be cross section area of copper conductor for carry 2000 amps & 2500 amps....sq.mm.?/
what is the relationship between current&voltage in practical purpose ?
Why the colour of insulator is always is chocolate in colour?
Why do we choose 33kV transmission for industrial purpose and 11Kv for township?
how will calculate the winding ohmic value in 3phase motors in h.p wise? ex.10 h.p motor winding value ph to ph ? 5 h.p motor any calculation please send me.
3- What is the target from Zero Impedance, Single Phase Imp., S/C Imp. and magnetic balance tests?
1. What is differential relay? How it operates? 2.How to calculate the Short Circuit Impedance in Transformer? 3.What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works? 4. While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply? 5. What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer? 6. Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example? 7. Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient? 8. What should be the minimum and maximum ohmic value for earthing? 9. Why DC Currents are not used in transformer? 10. What is the Frequency while we step up the voltage from 220V to 11KV? Is it possible? Explain it?
Is it benefitial to supply 210v ac to lighting fixtures instead of 240v ac?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)