I have three phase 400 KW,390 A MOTOR.For this motor which type
of Cable is required....specifically rubber cable required. Can
anyone help me..
Answers were Sorted based on User's Feedback
You mentioned the current capacity of motor is 390A, If
distance is too closer to the breaker,then you might be go
for copper cable, it will have lesser cross section and
high current carrying capacity. If the distance is more
better to go for the Aluminium cable so that cost of the
cable will reduce from the copper cable.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / abhishek
dude you have not mentioned the rated vol of the motor
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / padmakumar
Cable size selection is dippending on several factors like
current,distance,cable routing, nature of load,duration of
running of equipment etc.Normally 400KW LT motors nobody
prefers to run due to high current handling.HT motor is
preferable.In case of LT, you can go ahead with 400sqmm two
runs of Alumonium cable with stardelta starter.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ramjilal
first your question is wrong 400 KW motor current more than
390 amps. second you not mention type of starter.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bhupat chaudhari - adani
you should be going with 400 sq al xlpe cable for long
distance and with star-delta..
Is This Answer Correct ? | 0 Yes | 0 No |
How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations
what is the breaking capacity and making capacity of circuit breaker and how
what is load balancing. what maximum load diffence is allowed between phases.
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
Explain the advantages and disadvantages of thermal power plant?
How a Universal motor works in Both A.C and D.C? What is the constructional difference with other single phase motors?
tell me about your project
hi frienda We have 750kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
i have attended the interview on 4th June,08 at Kolkata in IOCL, can anybody tell me what is its result
why is fan rotating slow speed, what is the problem?
when the supply of MSEB is cut off & all the load of the industry is driven on generator at that time the capacitor which is connected in industry for power factor control is switched off why?
How to control the dc motor in ac supply without thyristor circuit?