Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have three phase 400 KW,390 A MOTOR.For this motor which type
of Cable is required....specifically rubber cable required. Can
anyone help me..

Answers were Sorted based on User's Feedback



I have three phase 400 KW,390 A MOTOR.For this motor which type of Cable is required....specificall..

Answer / sindhejs

You mentioned the current capacity of motor is 390A, If
distance is too closer to the breaker,then you might be go
for copper cable, it will have lesser cross section and
high current carrying capacity. If the distance is more
better to go for the Aluminium cable so that cost of the
cable will reduce from the copper cable.

Is This Answer Correct ?    2 Yes 0 No

I have three phase 400 KW,390 A MOTOR.For this motor which type of Cable is required....specificall..

Answer / abhishek

dude you have not mentioned the rated vol of the motor

Is This Answer Correct ?    2 Yes 0 No

I have three phase 400 KW,390 A MOTOR.For this motor which type of Cable is required....specificall..

Answer / padmakumar

Cable size selection is dippending on several factors like
current,distance,cable routing, nature of load,duration of
running of equipment etc.Normally 400KW LT motors nobody
prefers to run due to high current handling.HT motor is
preferable.In case of LT, you can go ahead with 400sqmm two
runs of Alumonium cable with stardelta starter.

Is This Answer Correct ?    1 Yes 0 No

I have three phase 400 KW,390 A MOTOR.For this motor which type of Cable is required....specificall..

Answer / ramjilal

first your question is wrong 400 KW motor current more than
390 amps. second you not mention type of starter.

Is This Answer Correct ?    1 Yes 0 No

I have three phase 400 KW,390 A MOTOR.For this motor which type of Cable is required....specificall..

Answer / bhupat chaudhari - adani

you should be going with 400 sq al xlpe cable for long
distance and with star-delta..

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Transformer Secondary maximum current (max. load)

3 Answers  


what are the main components of fan?

2 Answers  


Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?

6 Answers  


WHY DISEL GENRATOR SET SHUT DOWN IN OVER LOAD CONDITIONS

5 Answers   HMT,


What is error of a measurement?

0 Answers  


What will happen if i connect two 3-phase tranformers secondary supply on one bus bar that is R-Y-B-N?

2 Answers   GMR,


Why the ceiling fan has three blades, why not two,four or five?

4 Answers  


what is ten delta ?

2 Answers   ABB, Areva,


what should be distance between two electrical earthing pit as per i.e.e

13 Answers   Badve,


what is servo motor and how it works?

0 Answers   Godrej,


what is the acceptable insulation resistance for motor/transformer?

2 Answers   Reliance, Tata Motors,


Who many reason of ignition fail ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)