I have three phase 400 KW,390 A MOTOR.For this motor which type
of Cable is required....specifically rubber cable required. Can
anyone help me..
Answers were Sorted based on User's Feedback
You mentioned the current capacity of motor is 390A, If
distance is too closer to the breaker,then you might be go
for copper cable, it will have lesser cross section and
high current carrying capacity. If the distance is more
better to go for the Aluminium cable so that cost of the
cable will reduce from the copper cable.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / abhishek
dude you have not mentioned the rated vol of the motor
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / padmakumar
Cable size selection is dippending on several factors like
current,distance,cable routing, nature of load,duration of
running of equipment etc.Normally 400KW LT motors nobody
prefers to run due to high current handling.HT motor is
preferable.In case of LT, you can go ahead with 400sqmm two
runs of Alumonium cable with stardelta starter.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ramjilal
first your question is wrong 400 KW motor current more than
390 amps. second you not mention type of starter.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bhupat chaudhari - adani
you should be going with 400 sq al xlpe cable for long
distance and with star-delta..
| Is This Answer Correct ? | 0 Yes | 0 No |
Transformer Secondary maximum current (max. load)
what are the main components of fan?
Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?
WHY DISEL GENRATOR SET SHUT DOWN IN OVER LOAD CONDITIONS
What is error of a measurement?
What will happen if i connect two 3-phase tranformers secondary supply on one bus bar that is R-Y-B-N?
Why the ceiling fan has three blades, why not two,four or five?
what is ten delta ?
what should be distance between two electrical earthing pit as per i.e.e
what is servo motor and how it works?
what is the acceptable insulation resistance for motor/transformer?
2 Answers Reliance, Tata Motors,
Who many reason of ignition fail ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)