how will you calculate rated Primary and Secondary voltage and
Current for 2500 KVA, 11kv/443V Transformer
Answers were Sorted based on User's Feedback
Answer / rajutadhikari
Rated current on HV side:
Irhv = P/ (1.732 * V) = 2500k/ (1.732*11k) = 131.22 Amps
Rated current on LV side:
Irlv = P/ (1.732 * V) = 2500k/ (1.732*0.443k) = 3258.28 Amps
Is This Answer Correct ? | 12 Yes | 1 No |
Answer / amit bose
primary I =(2500*1000)/(11*1000)
Secondary I= (2500*1000)/443
Is This Answer Correct ? | 1 Yes | 3 No |
Why high Voltages come in multiple of 11, like 11 KV, 33KV, 66 KV, 132 KV etc.
What are various impedence in any machine
2 Answers Engineers India Limited, NTPC,
What is big transformer parts and their function ? Ty
why the arc welding machines require parallel earthing systems? ie why each machines are connected to earth pit by separate wires during earthing? wats it adavantages?
what are the basic concept to design a out door Substation?
1.Why use in ups in software's,reason,and pls explain. 2.what is the isolation transformer and main use it's functioning and partes.
if we use contactor & MCCB both in a feeder.in this feeder rating of contactor is higher or lower or same of MCCB rating & why?
In view of Electrical Engg. What is the use of SCR(Silicon control rectifier)
Why DC current is not used in transformer?
electromechanical relay type identification example : type=tjmh t-stants for j- m- h-
Q-1 what are the structural and operational difference between a distribution and a power transformer? Q-2 what is skew in motors? Q-3 draw equivalent circuit of transformer Q-4 explain with phasors how pf is improved with loading in induction motors Q-5 DIFFERENT METHODS OF CABLE LAYING(interviewer asked if i heard new chemical based earthing system next) Q-6 pi model of medium length trans line Q-7 v/f control?why Q-8 vacuum circuit breaker operates in?
Why in medium voltage system(3.3kv to 33kv, neutral is earthed with either resistance, reactance or neutral grounding resistance?