in the boiler in the main steam line and its bypass line and
the startup vent vales are only motorised valves why cant we
use other types of valves such as pneumatic.
Answers were Sorted based on User's Feedback
The design engineers must have had a reason why they
selected to use motorized valves in stead of pneumatic
valves. It might be that they felt the main power is less
likely to fall away than the plant air compressor tripping
and there is no air to operate these valves. It also
sometimes happens that the main instrumentation supply UPS
(24VDC) will trip and the whole plant looses the
instrumentation supply but the main supply is still available.
Also if the main power do fall away there is always the
emergency generators that will kick in and supply emergency
main supply to all the critical systems.
Just for interest they tend to select motorized valves for
safety systems as well like foam, fire pump control valves
and deluge main control valves, most probably for the same
reasons.
Good luck
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / rajender
For Very high Pressure Applications motorised valves are
used.
| Is This Answer Correct ? | 1 Yes | 2 No |
What is the syllabus for Instrumentation Engineers, who wish to join the Public Sector Units??
Can a Differential Pressure Transmitter be used as a normal pressure transmitter??
hi i'm an Instrumentation student,i have one doubt that we can call- > computer science as CS > Information science as IS > Electronics & communication as E & C In the same way what is short term for Instrumentation....?
What pressure transmitter.
how we can check level probe and controller
what are the use of belew gear in general ??
if change the pid in D value so what action.
I have completed B.E. Instrumentation & control in 2009. i have 3 year industrial job experience in chemical plant.now, I want to join M.E. in external. so, Plese say easiet way and good institute name.
explain the working of Coriolis Flowmeter.
what is the difference between scaler and vector drive
how to measure the output of RTD given the general formula of rtd.
How to calculate the flow rate in Vortex flow meter?What is K factor?Can you give me an example calculation to understand the same as better?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)