how to measure the output of RTD given the general formula of rtd.
Answers were Sorted based on User's Feedback
RTD's output is resistance.
As we know RTD means resistance temperature detector, so we measure resistance across the terminal of RTD by multimeter.
Now assume measured resistance is "X" and RTD we are using is PT100 then,
T(temp)=(X-100)/(0.386)
*PT100 RTD shows 100 ohm at 0°c
Is This Answer Correct ? | 17 Yes | 0 No |
Answer / rajesh.
RTD is Resistance Temperature Detector. As temperature varies resistance also change. So the output of RTD is Resistance. Which in terms converted into current (4 – 20 ma) by means of Transmitter. Generally RTD is available as Pt100.
Pt100 means 100OHMS at 0’ C for a platinum resistance bulb.
Formula for RTD:
Rt. =Ro (1+α t)
Rt. =Resistance of zero temperature.
α = Co. off of thermal (expansion)
t = temperature to be measured.
Example:
Calculation of Resistance or Pt 100.
Ro. = 100
α for platinum = 0.00385/c.
To calculate Resistance at 100’c
R100 =100(1+(38.5*104*100))
100+ (100*0.385)
R100 =138.5
Resistance at 100’c = 138.5
Is This Answer Correct ? | 4 Yes | 0 No |
Why DP transmitters are subjected to high static pressure test of 100 bar. Though they will be used for very small pressure range
for indiacation of turbine(china) bearing temperature what type of sensor will be used(i.e. rtd or thermocouple or themister ) ? why it is ? i need clear explanation ?
How to check vortex flow meter is in good condition while we do not having calibration setup?
our kks tagging is crossing more than 12 character please suggest how to take tags in the DCS
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
Difference between ultra sonic flow meter
Air pressure in a pressure vessel can rise or fall at up to 2.5kpa/s.The pressure is sampled every 0.5 seconds.If range of the the pressure indication is 0 to 1500 kPa, what is the max value of the error due to sampling in % of Span
What is sensitivity in vibration probes..?
How to calibrate the flow transmitter
What different types of problems do occur while doing the loop checking? and please explain in detail or mail me at kadam.aniket143@gmail.com
1 Answers Operational Energy Group, Process Control Technologies,
why use to 250 ohm for hart protocol and why hart communicator not communicate without 250 ohm
generally for transmitter we are giving supply 24vlts?but we are getting output 4-20ma ? how it is possible? is there any operation inside the tx?pls give complete information?