Answer Posted / ramesh
1 Hp = 746 watts
10 Hp Motor
10*746=7460w
so 7460 w is the power drawn by 3-ph motor. and three phase
voltage is 415 voltage.
so I = P/root3*v*pf*eff
i=Wattage/1.732*415*0.8*0.85
=7460/1.732*415*0.8*0.85
=7460/489
=15.25A
| Is This Answer Correct ? | 78 Yes | 18 No |
Post New Answer View All Answers
What id difference between power and energy?
sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah
1)what is the function of a frequency inverter? 2)If a few frequency inverter are connected onto a device network,what are the two setting that will ensure the frequency inverter work properly on the network. 3)whats is the name of the input sensor for weigher? 4)How to confirm that the load cellis faulty? 5)Describe briefly the steps to validate that the weigher is working properly? 6)Describe the procedure to validate the flowmeter accuracy? 7)Describe briefly the steps to validate that the tempreture sensor/transformer is working properly. 8)what is the adjustment that need to be done when you are calibrating the temperature transmitter ? 9)what are the safety measures to be taken before disconnecting motor for rewinding. 10)whats is the synchronous speed in rpm of typical 4pole 50hz motor? 11)whats is the formula for kw, ohm's law 12)if a 3phase motor is rated 3kw,415vac,what is it's rated ampere?
How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?
What is A check, B check, C Check & D check for a diesel Generat
What test must you do before powering up a circuit that you have been working on?
why the India electrical supply transmission loss is high when compare to us
kVA rating of ordinary transformer is increased when connected as an auto transformer because A transformation ratio increased B secondary voltage increased C energy is transferred both inductively and conductively D secondary current increased
What is the percentage loss for aluminium wire for HT line more than 11KVa
State thevenin’s theorem?
What is difference between slip rings and carbon burushes?
draw a circuit diagram connecting transformer OLTC- RTCC- VCB-Marshalling Box otherwise Explain in words
Give some differences between open loop and closed loop?
what is the affect of earth's magnetic field on the frequency used in aircraft???
A 3 phase transformer's (Y-Y) Y and B phase is (Y and B connection not broken) broken from neutral and R and Nutral connection is ok, what will be the relay tripping and why