In any industrial plant there will always be good records
and documentation on all equipment as well as all
instrumentation installed on the plant. The easiest in your
case is to find the FT tag number on the P&ID drawings or
the CCR faceplate and look at the data sheet of the missing
transmitter. The original calibration in differential
pressure will be on there as well as the model number of the
transmitter you need.
All you then have to do is calibrate the new DPT with the
diff press as per the data sheet and it will work as before.
In most cases the squire root extraction is done in the DCS
and not in the transmitter so try it just like this first.

The faceplate in the CCR will normally be set up to display
the min and max flow so that will not help you to find the
calibration diff pressure of the transmitter.

You can also try and find the original transmitter that was
removed and put power on it ans see what it was calibrated
for before. Even if the transmitter is faulty it might still
be able to display information. The is just as a last resort
since you cannot be sure if this calibration is what it
should be and it is better to double check it with the
documentation. This is just a method to double check
information.

As a desperate measure you can also measure the upstream and
downstream pressure as it is now during normal operation and
calibrate your transmitter to 1,5 that differential pressure.
For example:
Say your upstream pressure before the orifice is 300Kpa and
downstream it is 270Kpa you therefore have a DP over the
orifice of 30Kpa during normal operation.
Calibrate the transmitter for 0 to 45Kpa.
The flow indication inside the CCR will indicate the correct
flow since the extraction and the display is already setup
as it was originally. Have a look at what the % the flow is
indicated on the CCR faceplate. Since it is normal
operations it should be about 50% of the scale on the
faceplate. If it is not, modify the DPT calibration until
the current flow display about 50% of the full scale in the
CCR. You should be pretty close then.
This is not a very good or accurate way to do it and you
should keep on looking for the original design specs and
then re-calibrate the DPT when you found it.
Good luck

Is This Answer Correct ?    5 Yes 0 No

there is one orifice plate already installed on 3" line, but my previous engineer(who is not ..

Answer / jigaranadkat

Dear Nitin,

Ideally you shall have all the records, but in case if you do not have the records then try to recalculate the DP value using orifice sizing. You can get data for process condition from your process engineer and B (beta value / bore i.d. from orifice plate itself).

If you do not know how to calculate DP the please forward all the process condition with Line size, Line schedule and B beta value to anadkat.jigar@gmail.com. I can recalculate it for you.

Hope this will help you out.

Best Regards,
Jigar Anadkat
anadkat.jigar@gmail.com

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

how to calibrate control valves & power cylinders & ultra sonic level transmitters

0 Answers   ABB,


how the arrangement of equipments done in control room

0 Answers  


We are used ABB 800xa 5.1.please tell me how to instrall this.

1 Answers   TCCL,


How is automatic reference junction compensation carried out in temperature recorders?

0 Answers  


What is the SCAN time of a DCS/PLC? What is the typical value for scan time of DCS and PLC?

6 Answers   Essar, Gasco, Siemens,






what is the role of proportional in process control?

6 Answers   OGDCL, Trident,


what is input and output cards of plc needs to be hot swappable mean

1 Answers  


what are the pinciples & units of flow, level, temperature, pressure, quality.

1 Answers  


What is the three element? And how it work?

1 Answers  


how to convert MA in to measuring values..and how mwasuring values into MA ?..plz ansr.i have intervw

0 Answers  


With N nodes and B branches what will have a network ???

0 Answers   BSNL,


i am confusing about differential pressure transmitter as i seen so many DPTs in different ranges how can we calculate level and flow with mmh20 plz tel me

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)