what is the disadvantage of leading power factor...why can't
we use it (pf=0) for a long period of time?
Answers were Sorted based on User's Feedback
In case of load,it will result in negative voltage
regulation increasing the voltage.In case of generators it
has the de-stablizing effect on the system ,the pf of which
is always lagging.
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / g.tripathi
It will have negative voltage regulation effect generating
high voltage spikes on the load.Moreover it will again
increase the current of the system which will result in
more power loss
| Is This Answer Correct ? | 13 Yes | 1 No |
Answer / pandu
the main disadvantage of leading power factor is wating the
power
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / yawista
sir can you please explain further...what is wating the power?
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / k. s. rajiv
It results negative voltage regulation,again decreases
pf,high current,voltage spikes,power loss etc. In short all
these adversely affect load and network. So connect
capacitors individually to the load so as to be isolated it
whenever the load is turned off.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / romroxmal
It's unpractical to have a leading power factor in an
electrical distribution system in general because majority
of your loads especially motors and some rotating machines
are partly inductive loads. Just keep the power factor
lagging like 85 to 95% PF by automatic capacitor banks.
Efficiency and life expectancy of those said loads mentioned
will be diminished.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / n.silambarasan
the leading power factor is not used in resistive load
accept reactive power.the inductive load only need the
reactive power
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / guest
actually We cannot use the pf=0 , at least it should be some value. i mean to say,0.x to 1,
0.1 0.3 0.5 0.7 0.9 1 0.9 0.7 0.5 0.3 0.1
Lagging-> Unity <-Leading
Actually there are three power generated in an electrical system.
1. Active, real or true power which are expressed in kw = sqrt(3)*v*I*cosØ
2. Apparent power expressed in kva = sqrt(3)*v*I
3. Reactive Power expressed in kvar = sqrt(3)*v*I*sinØ
If cosØ(power Factor)=0.99 or -0.99, the sinØ will be same=0.14
If cosØ=-0.8 or 0.8, the sinØ will be same=0.6
If cosØ=-0.5 or 0.5, the sinØ will be same=0.86
According to the above values it is clear that if we go for lagging or leading pf the reactive power generated will be equal.
Kva= kw+kvar,
If use lagging or leading pf the real power (kw)we can use is same. So we must go for nearest value to unity pf to make Kva=kw(this condition satisfies only if Kvar=0 and pf=1) Finally more real power usage.
Then one of my friend told govt is advicing them to use leading power factor , its only because apart from the bulk consumers the domestic users wont use pf correction. In order to compensate we are said to use leading pf.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shareef
P= SQRT(3) * V * I * P.F
P.F= Cosin(AN)
AN= angle between V&I
If you are talking about P.F that means you are talking
about loads.
1- If P.F=1 that means the load is resistive load (its the
ideal case, the consumed power is active power only: MW)
2- If P.F=0 that means the load is inductive or capacitive
-(If the power is inductive that means the load will
consume power: +MVAR)
-(If the power is capacitive that means the load will
deliver power to the system: -MVAR)
In electrical systems the loads are resistive and reactive
that means the P.F value will be between 0 & 1
Examples
* If P.F = 0.9, its good for electrical system because it
is nearset the ideal case (the Voltage drop is less & the
voltage at end bus is within the limits)
* If P.F = 0.6, its bad for electrical system (the Voltage
drop is high & the voltage at end bus is out oflimits), in
this case we need to install capacitor bank to improve the
P.F and the voltage at end bus
Note. capacitor bank will deliver/give MVAR to the
electrical system
| Is This Answer Correct ? | 3 Yes | 6 No |
In practically it is not possible(i.e.power factor=0).If
Theoretically power Factor=0,means there is no actual
power(true power).(i.e.only wastage of power).
i think your i question is wrong pf=0 means lagging power
factor.
there is no disadvantage of leading power factor.
if lagging power factor means more wastage of power
| Is This Answer Correct ? | 6 Yes | 13 No |
why always out of the 3 phase(RYB) of supply, in Y phase w.r.t the voltage is higher? on R & B phase the voltage will be lower as compared to Y phase?
Wat is the best to use in a generator a 6.5kva or a 7 kw
What is nyquist contour?
HOW TO FIND OUT 1. LINE CURRENT, 2. PHASE CURRENT IN AN ALTERNATOR / TRANSFORMER WHICH IS FEEDING A I)STAR LOAD ii) DELTA LOAD, USING A CLAMP METER. NORMALLY WHEN WE USE CLAMP METER IN A DG SET THEN WHAT DO WE GET?? PHASE CURRENT OR LINE CURRENT.
What is difference between VCB and SF6 breaker
what is R Core Transformer. how it differs from normal transformers. dont search in net and post the answer.
Why Diffrential and Ref relays are used together although Diffrential relay can protect Pri and Sec of Transformer
sir am giving jspl exam on 19th oct . i belong to eee, so plz send previous question papers ..........to dis id abhilash203@gmail.com
Rated moter voltage and frequency is 380volt 60 hz but moter is running at 380votac 50hz is this harmful for moter winding
what is the contact resistance of sf6 circuit breaker??
Why High voltage are generate noise ?
what s a servo motor? how to control the servo motor? and its application, purpose of using?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)