Answer / karteek.k
there is an empirical formula to calculate voltage drop for
given cable, when you are given load in amps, i.e
(1.732x1.1xIxLxR)/1000.
1.732- square root of 3(because 3 phase circuit)
1.1- multiplication factor
I- load current in amps
L- length of the cablertee
R/1000 - resistance per kilometer
if u get voltage drop below 5% of the given voltage, i.e
415V, it will be optimum to use that cable otherwise we need
to go for next higher rating.
| Is This Answer Correct ? | 9 Yes | 0 No |
why use generator Earthing/Graunding.
Why CT secondary is grounded?
Is there a standard depth of gravel fill in Substation Switchyard? Please give a design/drawing. Thank you.
WHAT HAPPENS IF STARTER OF A FLUROSCENT LAMP IS SHORT CIRCUITED AND WE PUT THE SUPPLY ON?
I need the list of Universities who have summer intake for BS degree in Electrical Engineering.?
what instruments used for measuring of inductance and capacitance.
Why we use startor to the motor?
Two electric lamps 40 W, 220 V each are connected in series across 220 V. What is the power consumed by the connection?
A circuit breaker is a
Wht ar the reason for low voltage on consumer side?
using n1*n2 which type transformer is made; where n1 is primary turn and n2 is secondery turn
DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)