How to ensure vibration sensor functioning accordingly.With
out using an other sensor.
Answers were Sorted based on User's Feedback
Answer / erniprasad
By using Vibration Transmitter calibration equipment,fix
the sensor on the calibration equipment.Gap voltage shhould
be adjusted as per requierd.Power on the calibration
equipment and vibration transmitter and increase the
vibration as per range.check the output of the transmitter
in milli amps across millivolts generated as per
vibration.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / dosshoney
TK-3 is calibrator which is having simulation
option.Vibration sensor can be fixed at TK-3 and simulating
from field GAP will be measured on vibration monitoring
system. difference between simulation and measured gap will
be calculated,so entire loop we can check using of TK-3
calibrator
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / guest
sensor use in prevented functiion. sensor use in fire syes
team
| Is This Answer Correct ? | 0 Yes | 4 No |
can i use 1 sq mm insted of 1.5 sqmm cable cable length 600 mts under ground laying Cable carrying 24 vdc 4-20ma current
What are difference between automatic and manual control system?
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
Troubleshoot to the device level basic process control systems given the Process and Instrumentation Diagram?
Derive capacitance to 4-20ma conversion formula / relation in capacitance type pressure sensor?
difference b/w single acting and double acting actuator by using application only?
How the flow can be measured by using DP Transmitter?
How to fix back the valve actuator stem
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used? Please tell me its Calculation formula.
for indiacation of turbine(china) bearing temperature what type of sensor will be used(i.e. rtd or thermocouple or themister ) ? why it is ? i need clear explanation ?
What is the load line in control valve?
what is zenier barier and what means zone 1,zone 2,and zone 3
2 Answers Bapco Bahrain Petroleum Company,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)