how to syncronize two dg sets
Answers were Sorted based on User's Feedback
Answer / shri..
1) first start the both DG set.
2) Then check Phase sequence R,Y,B
3) check the LL voltage & LN voltage. (both DG voltage
should same)
4) Check The engine RPM (both engine RPM should same)
5) Check The Frequency (both DG Frequency should same)
6) Then close the both breaker.
7) then cross check the voltage,Frequency,RPM
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / santhosh
DG Sets with equal Voltage, Frequence and RPM should be
connected to a single bus with equal polarity and phase
sequence. Both the DG's should be protected with protecting
devices like breakers.
DG's should be operated in such a way that is starting only
one DG should get ON and as the load crosses 75% of the
capacity of DG then the second DG should get ON.
This will help in minimisng the consumption of fuel, Load
sharing and improves the performance of DG.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satender
you have first of all Start stop the DG's in manual mode ,
then check the voltage biasing and speed biasing by running
it on load ( single unit ) . Then check the phase sequence
of DG's and then give the synchroniizing command
| Is This Answer Correct ? | 2 Yes | 4 No |
I have AC automatic voltage regulator 15KVA What output currant?
How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me
If anyone would like to know or practice for FEWA papers contact me on mohamedrashad2@hotmail.com Just completed the supervisor exam in April 2021
Please help me.What are the difference between two wire, 3wire, and 4 wire in electric meter?
how to electronic energy metter failed in electomagnectic fild passing in the metter and which thing to defect more on metter.
How do you compute voltage drop and cable size over distance?
Can any one provide the inspection procedure of MIMIC for VFD panel? Details: If someone wants to have a mimic in the VFD panel what are inputs considered for the mimic(like on,off,trip) whether we are able to add speed variation in the mimic(if so how can we get) and what are the parameters to be checked in the MIMIC during inspection?
what is slip?
How to megger test 11 kV cable and the acceptance IR value
How can ignition voltage of light increased with the help of a ballast
What is the difference between PT for metering and PT for protection ?
IF HT CAPACITOR IN ON POSITION IS THERE ANY LOSSES I.S I SQURE OCCURS IN THE SYSTEM
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)