Answer / shri..
1) first start the both DG set.
2) Then check Phase sequence R,Y,B
3) check the LL voltage & LN voltage. (both DG voltage
should same)
4) Check The engine RPM (both engine RPM should same)
5) Check The Frequency (both DG Frequency should same)
6) Then close the both breaker.
7) then cross check the voltage,Frequency,RPM
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / santhosh
DG Sets with equal Voltage, Frequence and RPM should be
connected to a single bus with equal polarity and phase
sequence. Both the DG's should be protected with protecting
devices like breakers.
DG's should be operated in such a way that is starting only
one DG should get ON and as the load crosses 75% of the
capacity of DG then the second DG should get ON.
This will help in minimisng the consumption of fuel, Load
sharing and improves the performance of DG.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satender
you have first of all Start stop the DG's in manual mode ,
then check the voltage biasing and speed biasing by running
it on load ( single unit ) . Then check the phase sequence
of DG's and then give the synchroniizing command
| Is This Answer Correct ? | 2 Yes | 4 No |
why we use negative feedback in control system.
In domestic supply, when neutral touches earth the earth leakage trips. Does this mean that if the star (neutral) point of an alternator is earthed that power will flow to earth i.e. a direct short to earth?
What is the need for checking knee point voltage for CT's?
in a delta-star with neutral grounding on star side what will happen if one star limb got opened at star point
what should be the acceptrd value of winding resistance for 2.5MVA transformer
How to Convert Gen KW to H.T amps ?
How much load can take a 16 mm aluminum cable 3 phase
what is fault level in 66kV system?
I have experienced electrical maintenance HT ,but I completed be ECE ....can I apply c license or not ???? Pls help me friend s...
Why Indian Electricity frequency desined 50 Cycles as developed countrys are using high frequency with low voltage
How much ph is maintained of water electrolyte which is used in LRS for 1200 kw slipring induction motor ?
0 Answers AMS, JK Lakshmi Cement,
why bucholtz relay placed inclined in transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)