Answer Posted / shri..
1) first start the both DG set.
2) Then check Phase sequence R,Y,B
3) check the LL voltage & LN voltage. (both DG voltage
should same)
4) Check The engine RPM (both engine RPM should same)
5) Check The Frequency (both DG Frequency should same)
6) Then close the both breaker.
7) then cross check the voltage,Frequency,RPM
| Is This Answer Correct ? | 9 Yes | 1 No |
Post New Answer View All Answers
need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.
What is the name of the winding to which supply is given?
11 kV line deraction check by an Engineer.
Disadventage of cable-gland earthing if any ?
description with working of all parts of a Diesel generator???????
What is the Surge for 1.1 Phase Induction Motor(For Eg.1Hp) 2.3 Phase Induction Motor(For Eg.1Hp) 3.AirConditioner(For Eg 1Ton) 4.Refrigerator(For Eg 180Ltr or 160kW) 5.Induction Cooker 4. Ceiling Fan
what is the effect of higher value of GD???
If i have two 3000 kW motors and the whole facility requires a 10 MVA transformer. What would be better installing two 5 MVA transformers(one for 1 motor ) or just a single 10 MVA transformer for both of them. Give reasons for your answer.
What is the effect of atmospheric pressure & Temp; on efficiency of motor? Why NGR(Neutral Grounding Resistor) is used in 132/11 KV Transformer & how? What is the use of Auto T/F in Grid Station?
What is meaning of out of phase (making & breaking) capacity And how to calculate
What happens to a motor if it is connected in Delta connection
R=*ΒΆ l/a
at what basis/standard we have to arrive the current density of aluminium/ copper in busbar?
i m in need of current rating chart of heavy duty pvc/xlpe, cu/al cables. can somebody provide me? if yes, plz send me at ashish_patel111@yahoo.com
how to determine ct ratio in ht vcb?