Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why transformer ratinh is in KVA????/

Answers were Sorted based on User's Feedback



why transformer ratinh is in KVA????/ ..

Answer / arun.giit

as all the losses is in the form of power;and in transformer
iron loss is directly propertional to voltage(V) &copper
loss is propertional to current(I).it is not depend upon
powerfactor,so it's rating is in KVA.

Is This Answer Correct ?    20 Yes 1 No

why transformer ratinh is in KVA????/ ..

Answer / shaikh

Cu loss of transformer depends upon current I and iron loos
depends upon voltage V...So as we can say that the total
losses of the transformer depend upon VA (volt-ampere) and
independent of phase angle between V & I (i.e. pf
angle)...so transformer rating is in kVA & nt in KW...

Is This Answer Correct ?    14 Yes 0 No

why transformer ratinh is in KVA????/ ..

Answer / tin`

Becuase kVA is the 'total' apparent power. The load
connected to the transformer can have different power factor
(pf) and so the kW rating will vary according; kW=kVA*pf.
The transformer rating is stated in kVA in order to show
the full capacity of the transformer and then the real
power (kW) rating can vary with power factor.

Is This Answer Correct ?    1 Yes 0 No

why transformer ratinh is in KVA????/ ..

Answer / salim

bcz
kw=kva×pf and load on tranz.is not constant.So pf is varies with load.thats why traz.rating is always in kva not in kw

Is This Answer Correct ?    1 Yes 0 No

why transformer ratinh is in KVA????/ ..

Answer / mohan singh

Transformer ratings are in KVA because the power factor is
for the load on which transformer will operate is not known
in manufacturing and KW = V x I x Cos Phi.so it is Rated in
KVA and not in KW.

Is This Answer Correct ?    1 Yes 1 No

why transformer ratinh is in KVA????/ ..

Answer / peter

coz KW or HP makes no sense.....transformer is not a power
conerter involving mechanical energy.....i mean...it just
transfers electrical energy ....

Is This Answer Correct ?    1 Yes 4 No

why transformer ratinh is in KVA????/ ..

Answer / bob

Because transformer is power source and active power and
reactive power drawn from it depend on load nutural.

Is This Answer Correct ?    1 Yes 5 No

why transformer ratinh is in KVA????/ ..

Answer / suresh

Because transformer have electrical output

Is This Answer Correct ?    2 Yes 10 No

Post New Answer

More Electrical Engineering Interview Questions

If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma

0 Answers  


What is the name of the winding to which supply is given?

0 Answers  


why the electric train touches only one conductor n where is the neutral n it will be running 3-phase or 1-phase?

3 Answers  


what is the full form of KVAR

6 Answers  


What is Electrical Engineering?

13 Answers   L&T, NTPC, Wockhardt,


what is the difference between the voltage of 5 volts capacitor and and 5volts battery?

0 Answers  


Dear Respected sir how to test ABB REX521 protection relay by relay tester.

0 Answers  


Do these factors (settling time, peak time, steady state error, overshoot, rise time, MPOS (Maximum percent over shoot)) are the part of first order, second order, higher order, linear, non-linear, open-loop, closed-loop, homogeneous & non-homogeneous systems ?

1 Answers   Limton,


diff. between star, delta connection?

4 Answers  


What is cable gland,why does use for?

5 Answers   ABB,


How do determine the Size of a Droop Current Transfomer for Paralleling of Two Generators, Say I need a Droop Current transformer for a 600 kW generator need to be parallel with a 800 kW generator, etc.

2 Answers   JK Cement, MPPGCL Madhya Pradesh Power Generating Company Ltd, PNG Power,


Why soda is added with water in Lrs of Sliipring motor…to Increase or decrease resistance of water?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)