why transformer ratinh is in KVA????/
Answers were Sorted based on User's Feedback
Answer / arun.giit
as all the losses is in the form of power;and in transformer
iron loss is directly propertional to voltage(V) &copper
loss is propertional to current(I).it is not depend upon
powerfactor,so it's rating is in KVA.
Is This Answer Correct ? | 20 Yes | 1 No |
Cu loss of transformer depends upon current I and iron loos
depends upon voltage V...So as we can say that the total
losses of the transformer depend upon VA (volt-ampere) and
independent of phase angle between V & I (i.e. pf
angle)...so transformer rating is in kVA & nt in KW...
Is This Answer Correct ? | 14 Yes | 0 No |
Answer / tin`
Becuase kVA is the 'total' apparent power. The load
connected to the transformer can have different power factor
(pf) and so the kW rating will vary according; kW=kVA*pf.
The transformer rating is stated in kVA in order to show
the full capacity of the transformer and then the real
power (kW) rating can vary with power factor.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / salim
bcz
kw=kva×pf and load on tranz.is not constant.So pf is varies with load.thats why traz.rating is always in kva not in kw
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohan singh
Transformer ratings are in KVA because the power factor is
for the load on which transformer will operate is not known
in manufacturing and KW = V x I x Cos Phi.so it is Rated in
KVA and not in KW.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / peter
coz KW or HP makes no sense.....transformer is not a power
conerter involving mechanical energy.....i mean...it just
transfers electrical energy ....
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / bob
Because transformer is power source and active power and
reactive power drawn from it depend on load nutural.
Is This Answer Correct ? | 1 Yes | 5 No |
What is different between DOL(Direct on line starter), VSD, S/S(Soft starter), and A/T(Auto Transformer)
how make megger test for control cable like 12c x 1.5mm and what it apply voltage and test timing details.
Why Trasformers rated in KVA
13 Answers College School Exams Tests, HAL, Oil and Gas Jobs,
Why CT secondary should not be kept open?
Why did call copper as a electrical conductor?
suppose i have two single and three phase induction motor,thier have not any rating on its panel,anybody can tell me which motor is single or three phase?
Explain principle of Soft-starter & how its working???
i want bhel placement paper for electrical if anybody having pl send to my id kavitha867@myway.com immediately
In hydel power plants, L.A's, S.C's are placed inside the control panel boards. what is the purpose? [already the total body was earthed to ground.]
working of diesel generator ?
three owners X, Y, z owned some tractors with them, on the first month x gave away the same amount of tractors to y and z ( as much as they possed), similarly in the 2nd month y gave of to x and z similarly by third month z gave to x and y. after this all X, Y, Z had 24 tractors each.
can we use breather in a SEALED power or distribution transfomer instead of injecting nitrogen.