How to measure Flow of air line,what is the procedure of
creating DP in line to measure Flow!
Answers were Sorted based on User's Feedback
Answer / touch2gobi
We can’t measure the flow value directly.
First create diff pressure in flow line using orifice,
annular pipe, venturi meter etc…
Then measure the diff pressure using any diff pressure
transmitter take square root get flow value.
Flow value = Sq.Root (Diff Pressure)
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / goldknight3000
First of all, you have to create a restriction in order to
create a DP. There are several types of doing this and the
most common is by using an orifice plate. You can refer to
ISO 5167.
Is This Answer Correct ? | 4 Yes | 0 No |
thru which signal does µP communicate with memory
how u meassure room temp?is it possible 2 meassure room temp by rtd or thermocouple?between rtd n thrmocouple which is more regard?3 meassure diff. between rtd n thermocouple?
what is dry leg and wet leg in transmeter calibration?
EXPLAIN NETWORK COMMUNICATION ON DCS?
What is the standard height for stancion supports? and what is the standard mounting height for different transmitters?
how can we tune a PID. If it is by zeiger nichols method..please explain briefly with help of an example.
what is difference between PLC and DCS?
Calibration procedure for Electro magnetic Flow meter
How to calibrate Toxic gas detector?
I have a steam flow DP transmitter that has output swinging. Steam valve is in manual.I have good steam pressure. The impulse lines have steam tracing on them. The steam tracing has a hole in it that is blowing raw steam on the high side impulse line only. Could this be causing the swinging?
Draw symbols of the following :
hi this is noor in my work spot, i arranged THERMOCOUPLE in the place of RTD. (in FEED WATER tank). can i use T/C or not?