What should be the ideal tapping location for pressure
differential transmitter for liquid service. If the tapping
taken from the top of the pipe then PDIT will work properly
or not. If PDIT do not work properly then what minimum
corrective action should be taken in order to solve wrong
tapping locations.
Answer / nilesh
1.Ideal tapping location for liquid flow transmitter
orifice tapping in horizontal line is horizontalplane or 45
Degree downwards.
2.If tapping taken from top of the pipe then gases in
liquid service can disturb the measurement and hence
control.
3.Tamperory solution for fluctuation is frequent flushing.
| Is This Answer Correct ? | 4 Yes | 0 No |
how many parts of valve positioner?
rtd principle?thermocouple principle?
Why we. Don't measure current in parallel? Why we measure current in series and why we measure voltage in parallel only?
2 Answers Almeer Technical Services,
which type of filter gives the constant phase characteristics?
What is micromotion transmitter? What is the porpose of using this transmitter?
T.x range -0.1 to 0.2 milibar,so how much mili ampear at 0.1 milibar?
How to measure Flow of air line,what is the procedure of creating DP in line to measure Flow!
IF ASK IN THE INTENVIEW WHAT TYPE OF BMS YOU USE?
what is cavitation ?
how to explain PID?
What properties or parameters to be taken into consideration for protection while selection of Dcs controller.
How hart protocol can be connected with control valves?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)