Answer / carl_ellis
The first PI proportional controllers were analog electronic
controllers. On those analog controllers, the integral
adjustment was a front panel rotary knob (or pot) which
adjusted the time constant of the error integrator circuit.
Integration is the mathematical operation on the error
signal in a PI or PID controller. Explaining how it works
as a calculus math function is meaningless to technicians
who haven't studied calculus.
Back then, the integral adjustment was called 'reset'
because the adjusting the knob was said to 'reset' the
process variable's droop back towards the setpoint.
Controllers were frequently recorder/controllers so the
trended PV action could be seen over time - the droop from
setpoint and the resulting reset towards the setpoint when
integral action was applied.
Hence, 'reset' became the term used for integral action
rather than 'integral'.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 0 No |
what is puling in n pulling out in flame scanner system?
In 2 wire transmitter 1 wire is used for power and other is used for signal( 4-20)ma In 4 wire transmitter 2 wires are used for power and 2 wires are used for signal (4-20)ma . but my question is "what is the criteria or parameters we have to consider while selecting these transmitters for eg( distance, safety zones etc.
how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?
how do u calibrate the vacuum transmitter if it shows more reading
how to measured k type thermocouple temp.
What is the diffrence between digital signal processing and discrete signal processing?
what is differential pressure transmitter and transducer? how to work?
how to trim the pressure transmitter ?
Make a ladder diagram on LSL valve will close, on PSL valve will open and start the motor
Hi Frnds , If Suppose 1 Pair cable of 1.5 sq mm is used for Transmitter and instead of 1.5 sq mm if i used 0.5 sq mm cable will the resistance change will occur and does it affect our transmitter reading. plz mail ur answer to ntnkamble@gmail.com plz immediately mail ur reply
what is the electrical operation procedure for switching on 27.6MVA electric furnace.
how to caluculate flow by using transmitter?tell me plz I am eagerly waiting for your reply..
2 Answers Agi Glaspac, Reliance Power,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)