What is Square Root Extractor for?
Answers were Sorted based on User's Feedback
Answer / shahzad
square root extractor is using for flow measurement
| Is This Answer Correct ? | 98 Yes | 11 No |
Answer / touch2gobi
Shahzad said only light answer....
We can’t measure the flow value directly.
First crate diff pressure in flow line using orifice,
annular pipe, venturi meter etc…
Then measure the diff pressure using any diff pressure
transmitter take square root get flow value.
Flow value = Sq.Root (Diff Pressure)
Any Comments, Please welcome (touch2gobi@yahoo.co.in)
| Is This Answer Correct ? | 59 Yes | 8 No |
Answer / leigh
In a differential pressure flow meter (orifice + DP Cell), pressure is measured before the orifice and after it. This pressure difference is used to measure the flow of the liquid in the pipe. If the pressure difference is more, the flow is more and vice a versa. The problem with this method is that the pressure difference is not proportional to the flow so if the velocity (flow) of the liquid increases, the pressure increases but at a different rate. If you were to plot this on a graph you would get a curve. This curve is not much good for auto control requirements. We have to make this curve straight or linear so that we can get a linear signal from the meter. A square root extractor is used to do this.
| Is This Answer Correct ? | 33 Yes | 2 No |
Answer / s. kanniyappan
Square Root extractor are used in Flow measurement in pipe
lines of low slurry and low viscous fluids by using Orifice,
Venturi, Annubar...
flow is measured by creating differential pressure along
those devices and taking square root extraction in either
transmitter side or in controller side.
some of the flow measurement devices like cariolis mass flow
meter, magnetic, vortex etc... which measure slurry and
highly viscous materials does not have square root extractor...
| Is This Answer Correct ? | 26 Yes | 9 No |
Answer / hasrat ali
normally,output of the flow transmitter will be in square
root scale, where the control valve opreate into a linear
scale.In order to change the square root output into a
linear scale we interdouce square root extractor which will
give the linear output to opreate the final control element.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / umar khayam
The relation between the differential pressure and the flow
is not leaner.the square root is used to linerize this
relation.u can calculate the flow of a dp flow transmitter
in % by using this simple formula (flow in %= 10(under root
of delta pressure in %)
| Is This Answer Correct ? | 16 Yes | 6 No |
Answer / nishat
flow is directionally proportionalto suare root of differencitial pressure
f=square root(p1 - p2)
so suare root extractor is used to solve the square root so that we could get correct flow
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ehtsam talat
DP & flow relation is non linear that is why square root is
used.it actually makes this relationship linear.
Q=10 under root Dp
Q=flow is %
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / dharmendra bhagwagar
The pressure differential over a distance represents potential energy (like a voltage), and the kinetic energy of the flow is proportional to the square of the mean velocity of the flow
Reference https://www.physicsforums.com/threads/i-need-an-easy-explanation-for-a-flow-formula.121914/
Reference https://www.physicsforums.com/threads/i-need-an-easy-explanation-for-a-flow-formula.121914/
| Is This Answer Correct ? | 0 Yes | 0 No |
sir i m preparing for BARC but i am not getting any papers to prepare for this exam so please send me some sample papers to my i.d for the preparation of barc.
what is compensation in engineering and what is temperature compensation?
why we use impulse line of flow transmitter at 45 deg. angle both side of orifice plate.
How is PH sensor works ?
A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic meter/hr. Thorough impulse line flushing and zero calibration has been done, yet problem persists. What do you think is the problem and how do you rectify this fault?
How flow control valve is working with pnuematic positioner and I/P convreter from command is given from remote
why to use 3 wire at RTD ? what's the reason for common wire ?
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
Working principle capacitance type level transmitter
in valve is constructed as per SME B 16.34, then which standard is used for fire testing of valve?.
what is the characteristics of control valve?
What is the difference between intrinsic instruments and ATEX instruments?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)