why to use 3 wire at RTD ?
what's the reason for
common wire ?
Answers were Sorted based on User's Feedback
Answer / prince
RTD's work on the principle of RESISTANCE. The two working
wires might have different lengths, so different resistance.
Third wire is used for compensating the extra resistance so as
to get accurate o/p. Third wire is in parallel connection with
one of the wire. In 4 wire RTD, the compensation is more.
| Is This Answer Correct ? | 13 Yes | 0 No |
Answer / carl_ellis
It is correct that an RTD indicates a change in temperature
by a change in resistance of an element.
The change in resistance must be monitored electronically
and any circuit connected to an RTD will include copper lead
wires which will add resistance to the circuit.
The problem is not that the lead wires will have different
lengths, the problem is that any copper lead wire has some
resistance which will contribute to a voltage drop from the
source current and appear to be the resistance of the RTD
element. Any contribution of resistance to the measurement
is an error.
Two lead wires connect to the RTD element and a 3rd lead
wire is used to compensate for the added lead wire
resistance so that the lead wire resistance is eliminated
and only the RTD resistance is measured and used to
calculate temperature.
Carl Ellis
Measure First
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / rathod mukesh r
If 2 Wire rtd use , The distance is more between remote location (Rtd) And dcs panle then error occur in reading of temperature. Means if wire length is increases then its own resistance also increase so proper reading is not transmited via 2 Wire. In 3 Wire rtd these error is remove using compensasion lead.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / yugesh shah
3rd wire is called compensation wire , when RTD is installed
far away from control room or where we get indication then 2
wire RTD fails to send appropriate sign al due to
temperature effect or atmospheric changes so 3rd wire is
helpful to send error free signals or resistance
| Is This Answer Correct ? | 0 Yes | 2 No |
how we calculate error in percentage when instrument calibrat
How vortex sensor used for steam flow measurment can be checked on line i.e without taking out from process line.
What is impulse line size
Why integral control mode call Reset controller?
What are the materials available to prepare individually for competetive exams in Instrumentation field? Plz reply...
Why 24VDC power Supply is used as standard for all loop powered transmitters?
What is the difference between intrinsic instruments and ATEX instruments?
what is thermo coupler and how it works
How to Calibrate Ultrasonic flow Transmitter in Field
what are the pinciples & units of flow, level, temperature, pressure, quality.
in control valve is constructed as per API 6D or API 6A, then which standard is used for fire testing of valve?.
flow transmeter accuracy 0.075% of full scale & find ucertainty is 0.025 % so what is maximum limit band of uncertainty
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)