how to convert transmitter milliamps output to like
temp,pressure etc.....
Answers were Sorted based on User's Feedback
Answer / nitin patil
i am giving here the formula for the same,
temp/ pressure = (ma - 4)* span / 16
where, ma = what you measured by multimeter
span = max range of the transmitter.
| Is This Answer Correct ? | 51 Yes | 6 No |
Answer / arun raja.s
Eg. you want to convert in DCS mean it for pressure
transmitter
field pressure Range : 0-100 Bar
Transmitter Calibration Range : 0-100 Bar so output 4-20
mA Depent on the Transmitter input pressure.
This output cable goto Analog input module, in DCS have
to set 0-100 Bar it work depent on 4-20 mA input.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / mastersensor80
the sensor in the transmitter sense the physical effect
(pressure/level/flow) in the transducer this effect is
converted to electrical effect where we can measure 4 -20
ma for example that on the transeducer and the sensor
part,but to answer the above question it is mainly as
answered by Nitin Patil it is merly calculation as the
forumla provided by Nitin.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / neeraj pundir
with the help of transducer we convert (temp,pressure) in
outputs milliamps signals.
| Is This Answer Correct ? | 5 Yes | 3 No |
Milliamps output can be converted to temperature or
pressure, by means of converting the amps to volt by placing
a 250ohm resister across the circuit.
| Is This Answer Correct ? | 11 Yes | 18 No |
Why 4-20mA SIGNAL IS PREFERRED OVEA A 0-10v signal?
is motorized valve closed when power shutoff?
What is the diffrence between digital signal processing and discrete signal processing?
tell how to calibrate a magnetic flow tx, vortex flow tx,dp flow tx,nozzle flow tx and venturi flow tx?
What is the difference between a double acting and single acting positioner? what type of valves use single acting positioners?
1 Answers AquaTech, NamPower, Samson Resources,
what is isloted barrier how it works and what are the main purpose.how it make safe area.
Difference b/w SCADA & DCS
can we create an interrupt in plc through scada?
the pump holds on run indication into the dcs and filed local control panel remote push button condition operaton wrong like when the push button pushing conditions the pump is off and the push button release condition the pump is on totally opposite condition . And control room inside give the stop command into dcs just 1secon relay engage and again normal condition. How can I slove
Decibel.
what is the significance of hook up
Where do we consider the pressure in mbar & where do we consider the pressure in bar & why is it so ?
2 Answers BOC, Jindal Steel and Power,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)