Answer / nitin patil
i am giving here the formula for the same,
temp/ pressure = (ma - 4)* span / 16
where, ma = what you measured by multimeter
span = max range of the transmitter.
| Is This Answer Correct ? | 51 Yes | 6 No |
Answer / arun raja.s
Eg. you want to convert in DCS mean it for pressure
transmitter
field pressure Range : 0-100 Bar
Transmitter Calibration Range : 0-100 Bar so output 4-20
mA Depent on the Transmitter input pressure.
This output cable goto Analog input module, in DCS have
to set 0-100 Bar it work depent on 4-20 mA input.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / mastersensor80
the sensor in the transmitter sense the physical effect
(pressure/level/flow) in the transducer this effect is
converted to electrical effect where we can measure 4 -20
ma for example that on the transeducer and the sensor
part,but to answer the above question it is mainly as
answered by Nitin Patil it is merly calculation as the
forumla provided by Nitin.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / neeraj pundir
with the help of transducer we convert (temp,pressure) in
outputs milliamps signals.
| Is This Answer Correct ? | 5 Yes | 3 No |
Milliamps output can be converted to temperature or
pressure, by means of converting the amps to volt by placing
a 250ohm resister across the circuit.
| Is This Answer Correct ? | 11 Yes | 18 No |
hii my name is sujith...i am preparing for HPVL GET 2010... so ,,,pls help me by send any previous questions or material to my site.....(Msujith_12@in.com) thank q
How to calibrate radar lt type transmitter
what are the problem's will accure in dcs or plc hadware and what are the solution for it?
Hot calibrate a level transmitter (wet & dry legs)?
what is basic working principle of Governer in power plant?
when an eddy current probe is installed inside of a turbine or compressor in case of probe problem same as:crash of head of probe,changing the scale factor because of low measuring gap(physical gap is ok(example=1.14mm)but voltage is reduced(example=-6 volts),is any way to check the probe,when the ohm of probe is ok.thank you,(Karim Tavakoli)
The performance of a pump is monitored by measuring the ________ and _________ pressures
Why we use negetive (-)voltage in vibration system
Coriolis flow meter coil supply is 24vdc but why still we given 230ac for this transmitter let me explained detailed review please
which type of signal used in instrument?
3 Answers Emco, Makson, Sail, TATA,
why we take %i0.0 as input for twido plc
what is mean by TDC-3000
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)