how to convert transmitter milliamps output to like
temp,pressure etc.....
Answers were Sorted based on User's Feedback
Answer / nitin patil
i am giving here the formula for the same,
temp/ pressure = (ma - 4)* span / 16
where, ma = what you measured by multimeter
span = max range of the transmitter.
| Is This Answer Correct ? | 51 Yes | 6 No |
Answer / arun raja.s
Eg. you want to convert in DCS mean it for pressure
transmitter
field pressure Range : 0-100 Bar
Transmitter Calibration Range : 0-100 Bar so output 4-20
mA Depent on the Transmitter input pressure.
This output cable goto Analog input module, in DCS have
to set 0-100 Bar it work depent on 4-20 mA input.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / mastersensor80
the sensor in the transmitter sense the physical effect
(pressure/level/flow) in the transducer this effect is
converted to electrical effect where we can measure 4 -20
ma for example that on the transeducer and the sensor
part,but to answer the above question it is mainly as
answered by Nitin Patil it is merly calculation as the
forumla provided by Nitin.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / neeraj pundir
with the help of transducer we convert (temp,pressure) in
outputs milliamps signals.
| Is This Answer Correct ? | 5 Yes | 3 No |
Milliamps output can be converted to temperature or
pressure, by means of converting the amps to volt by placing
a 250ohm resister across the circuit.
| Is This Answer Correct ? | 11 Yes | 18 No |
How many input(Analog and digital) and outputs(Analog and digital) are there in DELTA v DCS Version 7.0?
Profibus DP is a multi-master system. Would it work on RS-485 4W or not, and justify your answer
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
What is mean by AC voltage and DC voltage
what is difference between DO and DI
What is stripper & spilitter ? Diffrence in this.?
how to calibrate control valves & power cylinders & ultra sonic level transmitters
What are Sinking and Sourcing IO Cards
can u please give the exact ckt explaination of AC Drive related to industries.
What is voltage free(wet) and potential (dry) contact?
suggest a sensor to measure rapidly varying temperature?
Reason for capillary type dp level transmitter fluctuation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)