what is the difference between 3,4 wire RTD sensor?
Answers were Sorted based on User's Feedback
Your maths is not right but actually you are right, and the
temperature indication does not increase so significantly
that it is worth the effort to use a 3 or 4 wire RTD. It
might increase with something like 0,001Deg C so that is so
small you might as well say there is no difference in the
accuracy of a 2,3 and 4 wire RTD, using a local or smart
transmitter.
In the old days we use to use a 2 wire RTD in the field and
then run a cable say 200m to the temperature indicator. By
the time it gets to the indicator the temperature is
completely different from what it was in the field due to
the cable resistance that add itself the the RTD resistance.
We compensated for that by installing a 3de wire for the
sole propose to measure the resistance of the cable itself
and deduct that from the total resistance measured at the
temperature indicator.
So the actual resistance of the RTD as measured at the
temperature indicator is RTD - RLine1.(or [(Rline1/2)x2]if
you want)
With the 4 wire it makes it more accurate in that you can
now measure line one and line 2. The theory is that the one
line might have a small difference compare to the other line.
So the actual RTD resistance at the temperature indicator is
measured RTD - [(RLine1/2)+(RLine2/2)]
But since we all use the small compact local and smart
temperature transmitters these days, 3 and 4 wires are no
longer needed since the distance from the RTD to the
transmitter is only from about 50 to 500mm and but it seems
it have stayed due to some design engineer always saying,
why buy a 2 wire if you can get the 3 and 4 wire for just
about the same price. It will make the indication just more
accurate, but they never say by how much (0,001Deg C)
Good luck
| Is This Answer Correct ? | 10 Yes | 2 No |
the difference between is that,the third wire for 3 wire
RTD is used for lead compensation.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / rajendraa
in 3 wire rtd lead wire resistance s reduced to a grt extent, lead wire error s such that t s the difference of wires A&B(A s the wire connected to rdt & B with the R in bridge circuit). in 4 wire rtd, the lead wire error s completely reduced,it s mainly used for calibrations & is very costly...
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dinesh priyadarshi
RTD are used as 3 wire and 4 wire combination for following
reasons :
1) Lead wire compensation requird because this reduce the
error produce by the wire resistance
2) The distance also increae the error so to reduce the
errors we r using 3rth wire for lead compensation.
3) 3 wire and four wire lead compensation increase the
accuracy by means of resistance
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ng
there is lead resistance compensation in 3 wire RTD, where as 4 wire RTD is idle of lead resistance compensation as 2 wires are used for volt measurement and 2 wire for current measurement.there is no question of lead resistance error, it gives accurate result
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / niranjan
RTD is inherently a 2-wire device, A 2-wire RTD can be used with either a 3 or a 4 -wire instrument by jumping the appropriate terminals.3-wire instrument, a 4-wire RTD will not provide any better accuracy. If the fourth wire is not connected, the device is only as good as the 3-wire RTD; if the fourth wire is connected, new errors will be introduced. Connecting a 3-wire RTD to a 4-wire instrument can cause serious errors or simply not work at all, depending on the instrument circuitry.
| Is This Answer Correct ? | 1 Yes | 14 No |
what is the difference between Ethernet unmanaged and managed Switch?
how many types of viberation transmitter and how to calibrate and where use of vibration transmitter
How can we calibrate pressure and flow transmitter in the field(online)?
please can anyone tell me in detail, what's mean by open loop and close loop?
What is DCS?
Can someone give a detailed chart on the temperature ranges which can be measured by various temperature sensors.
What is possitive and negative feedback?
why we take 4 to 20 mA as out put of every instrument like pressure transmittre ?why we cant take 0 to 20mA as output?
Why Boiler Drum level transmitter (TX) or level transmitter rang always put -600 to 0 other -900 to 0. Mines range why useā¦.?
how to calibrate control valves & power cylinders & ultra sonic level transmitters
i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the same using DPT , SO WHAT WILL BE THE URV & LRV, DENSITY OF THE TANK FLUID IS 0.95. is there necessary to fill the LP side with fluid.
What is surge in compressors? How to detect and control it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)