Why Boiler Drum level transmitter (TX) or level transmitter
rang always put -600 to 0 other -900 to 0. Mines range why
use….?
Answers were Sorted based on User's Feedback
Answer / radha
this is called wet leg system,so you are telling range -600
to 0 means your drum distance between HP & LP 600 mm and HP
and LP legs both are filled with condensate(water)
continueosly but LP leg distance higher than the HP leg,so
LP side pressure will acting 600mmWC extra, compare with HP
leg pressure,so we have to eliminate that pressure LP
pressure 600mmWC
thats why -600mmWC = 4mA
0 mmWC = 20mA
| Is This Answer Correct ? | 23 Yes | 7 No |
Answer / automatic
the negative value used for wet leg level transmitter that
means, you have the HP side filled with a reference liquid,
a initialy you should entre the pressure value of this side
in considiration that's why when we isolate the transmitter
from the vessel we never drain the HP leg
| Is This Answer Correct ? | 15 Yes | 5 No |
Answer / mavdiyaamit@gmail.com
I allways -600 to 0 range is used because maximum vacuum pressure ranhe is -760 mmHg so not use in -900 to 0
| Is This Answer Correct ? | 0 Yes | 9 No |
1. How can leveltrol be installed in steam drum for measuring the level of steam drum?
what is working principle of presure and temperature guage?
what is the input of ph sensor and meter during the calibration time and what is the output?
Give me best instrumentation Books name..Ple...
Why only negative 24 vdc supply give in vibration measuring system.
thru which signal does µP communicate with memory
Thermocouple is a transducer but rtd is not transducer why? Both taking heat as a input and giving mv
sir, i preparing hpcl,ongc,barc,hal exams(instrumentation engg)pls send a placement papers
how to calculate range of level transmitter?
Which mechanical device is used in pressure gauges to reduce pulsating
what is orfics working in main steam line. is it increase pressure, velocity of steam flow and dicrease steam flow rate. or any other
How a pH sensor & analyzer work at waste water treatment plant, whats the principle & science is beyond this,How pH sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in analyzer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)