Why Boiler Drum level transmitter (TX) or level transmitter
rang always put -600 to 0 other -900 to 0. Mines range why
use….?
Answers were Sorted based on User's Feedback
Answer / radha
this is called wet leg system,so you are telling range -600
to 0 means your drum distance between HP & LP 600 mm and HP
and LP legs both are filled with condensate(water)
continueosly but LP leg distance higher than the HP leg,so
LP side pressure will acting 600mmWC extra, compare with HP
leg pressure,so we have to eliminate that pressure LP
pressure 600mmWC
thats why -600mmWC = 4mA
0 mmWC = 20mA
Is This Answer Correct ? | 23 Yes | 7 No |
Answer / automatic
the negative value used for wet leg level transmitter that
means, you have the HP side filled with a reference liquid,
a initialy you should entre the pressure value of this side
in considiration that's why when we isolate the transmitter
from the vessel we never drain the HP leg
Is This Answer Correct ? | 15 Yes | 5 No |
Answer / mavdiyaamit@gmail.com
I allways -600 to 0 range is used because maximum vacuum pressure ranhe is -760 mmHg so not use in -900 to 0
Is This Answer Correct ? | 0 Yes | 9 No |
Hello Friends do you know this answer of this Question? Which color you would use when there is Somthing not correct or need to change In P&ID? i mean color that use for highlight that need to update in P&ID. Yellow Highlighter ? Red color ? Blue Color ? Appreciate for your answer. Thanks Blue Color
What is shriking and swell effect for a boiler ?
what is the difference between Ethernet unmanaged and managed Switch?
what is all types of analyzer in water production plant?
Why flow/pressure transmitter before control valve?
How to check vortex flow meter is in good condition while we do not having calibration setup?
wt is cold junction compensation
What s the exact height of installed transmitter?
what is "smart" in smart transmitter ?
Which products are available in the Mass Systemswitch and System Manager AC range?
what is the function of 3 way manifold valve in a closed loop system?
what is the resource block mode in foundation field but ? what is advantages for this